Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52.

My question is I had a fault which I couldn’t find or rectify during a periodic test that I carried out yesterday (tenant property) occupied.

Circuit: Ground Floor Socket
32A Ring (r1 0.42, rn 16, r2 0.71)
R2 0.42 x 1.67 = 0.701 = Good above apart from rn!

Whipped all sockets off and checked connections at db of course. Couldn’t find anything at this point. Checked all points. Last thing was left was lifting floor boards. I couldn’t find anything in between (JB, interconnection, joint) I’ve asked tenant, unfortunately no relevant answer for an indication.

Carried out a long lead test CU - rn one leg (T&E) walked around - found dead leg from one point to the next that was giving 16ohms. Point A-B.

Split ring x2 radials (20A x 2 protective devices)

Carried out the procedural
Test R1/R2
R1/RN
Confirmed polarity….

Now getting voltage fluctuations and getting some sockets working and some aren’t due to not having 230VAC at every point on “Ground Floor Socket”

I believe there could be another dead leg or broken neutral, loose or lost.

Advice people? What would you?
How would you go about it?
 
Good approach so far.
Double check your CU connections just in case.
Sockets that aren’t working, test L to E for 230v to determine if problem is still the N.
Long lead test of all 3 conductors, also consider removing all accessories and IR test end to end.
I know this will/should give 0 but it can also occasionally “blow apart” the problem connection and make finding it easier (an old fire alarm service trick). If the test result suddenly rises, bingo!

There does come a point where re wiring a leg is the only sensible option - hopefully it won’t come to that!
 
Good approach so far.
Double check your CU connections just in case.
Sockets that aren’t working, test L to E for 230v to determine if problem is still the N.
Long lead test of all 3 conductors, also consider removing all accessories and IR test end to end.
I know this will/should give 0 but it can also occasionally “blow apart” the problem connection and make finding it easier (an old fire alarm service trick). If the test result suddenly rises, bingo!

There does come a point where re wiring a leg is the only sensible option - hopefully it won’t come to that!
Thank you bud. I’m loving this forum already being in communication with like minded individuals like yourself who can share knowledge.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Peterborough UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
If other, please explain
None
Business Name
Copiam Electrical

Thread Information

Title
Ring circuit fault, High RN
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
CopiamElectrical,
Last reply from
CopiamElectrical,
Replies
4
Views
1,680

Advert

Back
Top