Discuss 6mm TW+ for a 26 metre run ,32amp RCBO .Max load 4.5KW in the UK Electrical Forum area at ElectriciansForums.net
I get 2.5mm .But thinking of throwing in 6mmChapter 7 of the OSG has a list of standard circuits, most of the time I can select one from there without having to get the calculator out.
Why?I get 2.5mm .But thinking of throwing in 6mm
I have it left over !! . So its kinda extra money in my pocket And use more 2.5mm . Also if they change printer (Photographic) at alter date to a higher spec .This could be a 7kw load . Banging in a 6mm now might save timeWhy?
Fair do'sI have it left over !! . So its kinda extra money in my pocket And use more 2.5mm . Also if they change printer (Photographic) at alter date to a higher spec .This could be a 7kw load . Banging in a 6mm now might save time
The RCBO will ensure disconnection times are met, assuming an otherwise healthy circuit.At end of day it comes down to cable loading/capacity, volt drop and ‘will it turn off quickly enough’.
Looks like a tick for first two. Need Ze to tick last one.
I’d add that depending on Ze I get anything between 4mm to 10mm out of the cable sizing calculator, so if it’s at the limit of a TNS Ze it can really change things.
Sure but wouldn’t you agree it’s better if PFC is also high enough, two cracks at the whip then!The RCBO will ensure disconnection times are met, assuming an otherwise healthy circuit.
good pointSure but wouldn’t you agree it’s better if PFC is also high enough, two cracks at the whip then!
My point was really that a circuit design should take into account Ze, and I’ve doubts that Zs with 2.5 would be less than 1.1 ohms.
It might not be actually! I can’t immediately see why the pro certs calculator is rejecting 2.5. When I’m home later I’m going to need to satisfy my curiosity as at first glance Zs and volt drop are ok….good point
It'd be nice, but I personally wouldn't go out of my way using thicker cable to achieve that. Odds are that the overcurrent part will disconnect instantly anyway.Sure but wouldn’t you agree it’s better if PFC is also high enough, two cracks at the whip then!
It was a classic case of garbage in, garbage out. As above, with a 25 or 20 amp OCPD it jumps straight to 2.5mm.It might not be actually! I can’t immediately see why the pro certs calculator is rejecting 2.5. When I’m home later I’m going to need to satisfy my curiosity as at first glance Zs and volt drop are ok….
Reply to 6mm TW+ for a 26 metre run ,32amp RCBO .Max load 4.5KW in the UK Electrical Forum area at ElectriciansForums.net