At end of day it comes down to cable loading/capacity, volt drop and ‘will it turn off quickly enough’.
Looks like a tick for first two. Need Ze to tick last one.

I’d add that depending on Ze I get anything between 4mm to 10mm out of the cable sizing calculator, so if it’s at the limit of a TNS Ze it can really change things.
 
At end of day it comes down to cable loading/capacity, volt drop and ‘will it turn off quickly enough’.
Looks like a tick for first two. Need Ze to tick last one.

I’d add that depending on Ze I get anything between 4mm to 10mm out of the cable sizing calculator, so if it’s at the limit of a TNS Ze it can really change things.
The RCBO will ensure disconnection times are met, assuming an otherwise healthy circuit.
 
The RCBO will ensure disconnection times are met, assuming an otherwise healthy circuit.
Sure but wouldn’t you agree it’s better if PFC is also high enough, two cracks at the whip then!
My point was really that a circuit design should take into account Ze, and I’ve doubts that Zs with 2.5 would be less than 1.1 ohms.
 
Sure but wouldn’t you agree it’s better if PFC is also high enough, two cracks at the whip then!
My point was really that a circuit design should take into account Ze, and I’ve doubts that Zs with 2.5 would be less than 1.1 ohms.
It'd be nice, but I personally wouldn't go out of my way using thicker cable to achieve that. Odds are that the overcurrent part will disconnect instantly anyway.

We would presumably be dropping the breaker to 20A if going 2.5mm, so it should max Zs for that.
 
It might not be actually! I can’t immediately see why the pro certs calculator is rejecting 2.5. When I’m home later I’m going to need to satisfy my curiosity as at first glance Zs and volt drop are ok….
It was a classic case of garbage in, garbage out. As above, with a 25 or 20 amp OCPD it jumps straight to 2.5mm.
I just couldn't see it for looking earlier.
 

Reply to 6mm TW+ for a 26 metre run ,32amp RCBO .Max load 4.5KW in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi all, Planning on wiring my neighbour's summer house which will be 15 metres away from the end of the house (20-25 metres total distance from...
Replies
29
Views
7K
Hi all, I wonder if you might chuck in your 10 cents worth on this on? I have been asked to install electric heating in an office up on the 4th...
Replies
18
Views
3K
Toneyz
T
Hi With a standard 13 amp domestic uk 3 pin socket the max load is 13 amps i believe?. So does this mean that a DOUBLE socket would have a max...
Replies
26
Views
8K
Deleted member 26818
D
Hi guys, I'm recently qualified so naturally a bit hesitant on my first jobs so looking for advice as much as possible. I'm working as a junior...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock