Discuss 6mm TW+ for a 26 metre run ,32amp RCBO .Max load 4.5KW in the UK Electrical Forum area at ElectriciansForums.net
At end of day it comes down to cable loading/capacity, volt drop and ‘will it turn off quickly enough’.
Looks like a tick for first two. Need Ze to tick last one.
I’d add that depending on Ze I get anything between 4mm to 10mm out of the cable sizing calculator, so if it’s at the limit of a TNS Ze it can really change things.
The RCBO will ensure disconnection times are met, assuming an otherwise healthy circuit.
Sure but wouldn’t you agree it’s better if PFC is also high enough, two cracks at the whip then!
My point was really that a circuit design should take into account Ze, and I’ve doubts that Zs with 2.5 would be less than 1.1 ohms.
It'd be nice, but I personally wouldn't go out of my way using thicker cable to achieve that. Odds are that the overcurrent part will disconnect instantly anyway.
We would presumably be dropping the breaker to 20A if going 2.5mm, so it should max Zs for that.
It might not be actually! I can’t immediately see why the pro certs calculator is rejecting 2.5. When I’m home later I’m going to need to satisfy my curiosity as at first glance Zs and volt drop are ok….
It was a classic case of garbage in, garbage out. As above, with a 25 or 20 amp OCPD it jumps straight to 2.5mm.
I just couldn't see it for looking earlier.
Reply to 6mm TW+ for a 26 metre run ,32amp RCBO .Max load 4.5KW in the UK Electrical Forum area at ElectriciansForums.net
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Hi all, Planning on wiring my neighbour's summer house which will be 15 metres away from the end of the house (20-25 metres total distance from...
7K
Hi all, I wonder if you might chuck in your 10 cents worth on this on? I have been asked to install electric heating in an office up on the 4th...
Toneyz
T
Hi With a standard 13 amp domestic uk 3 pin socket the max load is 13 amps i believe?. So does this mean that a DOUBLE socket would have a max...
8K
Deleted member 26818
Hi guys, I'm recently qualified so naturally a bit hesitant on my first jobs so looking for advice as much as possible. I'm working as a junior...