Von Vardo

Went to a job today where the boiler is in an outhouse. The only metallic incoming service is oil from a tank outside.
Can I install a dedicated earth spike for the outhouse and bond the oil to that or do I need to bond it back to the MET in the house?

I'd be grateful for any advice on this.

Ed
 
Dont see why not, as long as you test the earth rod to ensure it falls within the correct parameters
 
You say the only incoming service is metallic, what about the outgoing, are they all plastic?
 
Yes, all pipework throughout the house is plastic, incoming water is plastic but oil is metal.
 
Will you isolate the CPC from the house at the boiler?
Will there be any earth paths from the boiler to thermostats?
 
Last edited by a moderator:
i would say that if the oil pipe is introducing an earth potential into the house then it needs bonding to the MET.
 
  • Like
Reactions: 1 person
I'm with Tel on this one, bond the incoming pipe to the MET. Assuming that there is no supply from the house to the outbuilding, for example feeding a pump (assuming this is gravity fed to the house).
 
The thermostat is wireless and CPC will be isolated from the house so this should be ok?
 
Outhouse only contains the boiler and a light (it's more like a shed!) - my thinking is to install a 2 way CU fed by SWA from the house, isolate SWA CPC and install a spike for the bonding and the circuits in the outhouse. Can you see any problem with that?
 
i'd prefer to export the earth!!! (going to bed now)
 
No that would be fine, obviously you will need RCD protection.
If you install a larger CU, then you would allow for the installation of a socket-outlet, either now or at a later date.
 
Why would you TT this outbuilding/shed?? Is it a PME supply to the main house??

Whether it's PME or not, you will still have to bond the service oil pipe as it enters the main house, if it is introducing an earth potential into the house.
 
  • Like
Reactions: 1 person
Why would you TT this outbuilding/shed?? Is it a PME supply to the main house??

Whether it's PME or not, you will still have to bond the service oil pipe as it enters the main house, if it is introducing an earth potential into the house.
Because installing a 10mm² bonding conductor from the shed to the house may be more expensive than installing a rod.
Does the oil service pipe enter the house, at the moment it appears to only go to the shed.
 
Oil pipe doesn't enter house - it IRS to the boiler in the shed from which all the pipework to the house is plastic. House is tt.
 
ah, you've only just mentioned that the pipework from the boiler to the house is plastic! i was thinking it was metal. in that case your original scenario is OK.
 
  • Like
Reactions: 1 person
bung in another rod.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Quick bonding question
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
26

Thread Tags

Advert

Thread statistics

Created
Von Vardo,
Last reply from
Engineer54,
Replies
26
Views
2,388

Advert