ringer
Was shown a PIR by a friend today where the Ze was recorded as 0.01 ohms. Not unexpectedly, the PFC was sky high at 19.9kA. I have never come across a Ze so low before. This is commercial premises, with a single phase TN-S supply. Now the nearest substation I am aware of is 150m away as the crow flies, or 250m away by road, which is more likely to be the route of supply cable takes from the substation to the property. Does a Ze this low seem likely at such a distance?
Was it an actual proper reading.
It is the devils own job normally to get a situation in a commercial premises where you can isolate the entire supply and take a reading.
Some do arrange shutdowns and take a correct reading, some may take a reading when the installation is on just to prove a path and many others make it up as they go along.
To be honest TD it will very much depend on the protection device on the main incomer which could be a BS 88 fuse for commercial.
If there are distribution boards around then those PD will dpend very much on the Zdb at each board
I think as others have said, perhaps where you tested isn't the origin of the return path ?
Maybe some parallel paths reducing your figure?
Are you physically able to see the earth strap coming off the casing of the incomer and confirm this what you tested ?
These measurements were made and recorded by someone else. I was just shown the PIR and had a quick look around. There are other issues with the PIR where recorded readings (or no readings were recorded!) do not ring true. Premises were in use at the time so was not possible to take my own readings. Hoping to get back soon when they are not open to do my own testing. I had remembered IQ's method for low values and intend to employ it. However I suspect that original reading for Ze was taken with bonding in place.
What I was asking originally was whether you might expect to get such a low Ze 250m away from the substation on a TN-S supply? The area is heavily built up with both commercial and residential premises.
If the standard of the paperwork is generally poor then I would wait to verify that Ze reading yourself before going too deep into the ramifications of it being so low. Could easily be a clerical error with a decimal point in the wrong place. My house is on TNS and has a Ze of 0.1.
Personally not had a reading as low as 0.01.
Site I work on has it's own TV network that is why they don't use MCBs specify that it has to be fuses.
Why's that then?? I know why to be honest, but that spec is based on cost effectiveness rather than anything else!! Having said that, HRC fuses can get mighty expensive, if you blow a few in the course of fault finding. Especially where some, will just replace the fuse without checking for a fault first etc... lol!!!
We use 22KA MCBs in a number of cases on our projects, in fact i can't remember the last time we have used fuses on the LV systems, can't say we use many fuses on the MV side of things either, apart from in the odd RMU and in the moving MV contact arms to voltage transformers in the main MV switchboards....
Customer is not rushing to sort this out, but wants to speak with me next week about it. Assuming for the moment that the measured value of Ze=0.01 ohms is correct, I am trying to establish what can potentially be done about this. To recap: TN-S, the DB circuit breakers are 6kA SCC, the DNO fuse is BS1361 type II 100A 33kA SCC, PFC is 19.9kA
So the DNO fuse will withstand the PFC, but the MCBs will not. Can we rely on the DNO's fuse to protect the installation? What about the potential for harm to the MCBs (and persons, livestock and property) at that level of fault current?
I would read the warning that all MCB manufacturers give regarding the PFC and MCBs
I've just re-read this thread, and it seems that the distance to the distribution TX is some 250 metres. We don't know the size of the TX though!! I would have to say that the supply cables would have to be sizable to allow a Ze of 0.01 ohm and a PFC of 19+KA. I would suggest that measurements taken have a largish error factor within them... You would only expect to see around 16KA in central London's DNO extensive networks.
250 metres is a fair distance, and when taking into account all the resistances/impedances of connections, switch gear, and cables etc, it's going to be highly unlikely that the given figures are anywhere near correct. Going by those figures the TX would have to be 1000 KVA, which would normally be capable of providing around 20KA into a fault at it's LV terminals, but very doubtful 250 metres distant, passing through all those said impedances...
To be totally honest, you would only find those figures within the actual sub-station itself or very, very close to it.
Took a while to get an answer to my original question, so thank you E54 for your last post! I was hoping someone was going to say that.
I hope to get the opportunity to take my own measurements sometime soon - I hate it when I suspect something is wrong, and cannot rest until i get to the bottom of it. My previous musings about SSC and HRC carriers were me trying to establish a plan B, just in case. Hopefully it won't come to that.
Reply to Ze and distance from substation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Another long one from me ... I hope that it covers all the bases and is a more thorough approach to the subject. It is my first design work so...
6K
G
Hi So today i tested at the orgin of the installation and on my MFT 1552 Megger, i got a reading of <0.01 for Ze and >19.9 KA for PFC, it's a...
7K