gareth020

Hi
So today i tested at the orgin of the installation and on my MFT 1552 Megger, i got a reading of <0.01 for Ze and >19.9 KA for PFC, it's a medium sized industrial unit and is fed from a substation about 30 meters away, so i expected it to be low. Obviously the client wouldn't let me switch off to disconnect the main earth, so i understand i would be getting parallel paths. But still does this not seem just a bit too low!?
As for the PFC, the main switch is 33KA rated and the mccb's inside the section board are 25KA so i guess they are all ok, but there are two Mccb's that are rated at 15KA, do i have to change these, or is it just the main switch KA rating i need to be concerned with!?
Finally My meter says greater than 19.9KA ...how do i find the actual value!? Or shall i just record this reading!?

Thank You
 
There is an excellent man on here called IQ, and a thread about just this. So instead of hunting through the forum i'm going to do it the lazy way.

If you PM IQ I'm sure he will have a link to the thread.

Just though to put your mind to rest, yes the parallel paths will give you a false lower reading. Remember our MFT are not as accurate as to show a realistic reading at such low levels.

IQ concocted a very good way to do this using a wander lead as a resistance in series with you meter and conducting the test using the cable resistance of the wander lead, this will bring your meter into a much better parameter. You then of course need to subtract the resistance of the waander lead and that will give you your Ze.

Of course you can't get a true Ze with the parallel paths, was this a PIR or an EIC
 
Hi
So today i tested at the orgin of the installation and on my MFT 1552 Megger, i got a reading of <0.01 for Ze and >19.9 KA for PFC, it's a medium sized industrial unit and is fed from a substation about 30 meters away, so i expected it to be low. Obviously the client wouldn't let me switch off to disconnect the main earth, so i understand i would be getting parallel paths. But still does this not seem just a bit too low!?
As for the PFC, the main switch is 33KA rated and the mccb's inside the section board are 25KA so i guess they are all ok, but there are two Mccb's that are rated at 15KA, do i have to change these, or is it just the main switch KA rating i need to be concerned with!?
Finally My meter says greater than 19.9KA ...how do i find the actual value!? Or shall i just record this reading!?

Thank You

Firstly, i agree with Malcolm, check accuracy of your meter at that level, IQ has a thread where he explains a method for greater accuracy.

Secondly, you need to see what the protective devices lets through at that level of fault current, i would expect a good degree of current limiting so even the 15ka rated devices may be ok.

I would need more info, the type of protective device, an accurate PFC reading and the breaking capacities of the equipment.
 
Firstly, i agree with Malcolm, check accuracy of your meter at that level, IQ has a thread where he explains a method for greater accuracy.

Secondly, you need to see what the protective devices lets through at that level of fault current, i would expect a good degree of current limiting so even the 15ka rated devices may be ok.

I would need more info, the type of protective device, an accurate PFC reading and the breaking capacities of the equipment.

I had thios on a domestic last week, posted a thread on it. IQ came up with some method of getting a better reading... Sub station is to blame..
 

Reply to Very Low Ze & Very High PFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
673
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock