Discuss When Is 0.5ohms Not 0.5ohms? in the UK Electrical Forum area at ElectriciansForums.net
forget its a socket and tell me how would you do the test (cooker point, spur etc ) your drop it forward and your point is really lost as what if the spur contacts are the same etc you would still miss them through routine testing.
An excellent point. Yes testing the socket front is picking up a fault you would never pick up with a fused connection unit to a fixed appliance or whatever. So is failing a socket for excessive Ze+R1+R2 measured at the front a True By The Book Failure or not? Probably not. Do you fail it in practice? Depends on the scenario I think. What is the risk if you don't fail it? A house fire, maybe. A dead family. What is the risk if you do fail it? Maybe an argument, maybe a client who doesn't use you again, maybe (depending on the contract) getting taken to court. This thinking inclines me towards failing it.
I admire anyone who goes this deep to understand their career
Only way I know how :)
These measurements are taken getting towards the arse end of the instrument's range.
Disagree. Measuring very low resistance is the bread and butter of the R Low Ohms range of the MFT and it has a calibrated accuracy capable of making the measurement, to an order of magnitude better than the 0.5ohm being measured.
Then there are all the errors to take into account, probe contact, etc. etc. etc.......
Yeah, I know, bimetallic voltages etc. But these should be catered for *within* the meter's tolerances in typical usage.
I have a socket that passes both R1 + R2 and ELI then i plug in a 30m extension that means the extension outlet falls well below pass value if i tested from it! ...where do i stand then???? We could go on forever here thats why i said you overthink this situe and subject to difference at front and back you kind of get an educated guess whether to recommend changing the socket.
I am not so sure on that statement, when I did my 2391 it was generally accepted that the measured Zs could be different from the measured/calculated Zs= Ze + (R1+R2), usually lower due to parallel paths.
Indeed, and that's the point, parallel paths can offer an unfair assist to help pull a Zs assessment down below the maximum value. Go back to basics - why when taking a Ze measurement at a DB do we not just clip onto the earth bar or MET, but instead have to whip out the earthing conductor and clip onto that? This is a standard assessment test/check in exams, practicals, Part P registration assessments and not doing it or not knowing why you do it is a good way to crash and burn. Not placing reliance on parallel paths in other situations is just an extension of that logic.
I did say there were two schools of thought on this, my own preferred is the "worst case method" measured Ze + measured (R1+ R2), thus not relying on parallel paths that may or may not be reliable, if this is compliant then I am happy, however I always record the actual measured Zs, unless it is impractical to do so.
BS7671 deems either method to be acceptable.
On an EICR it is quicker to do the measured, and just the R2 wandering lead method is usually sufficient, obviously proving polarity as well, horses for courses and whatever method is quicker or easier in a given situation.
But as I say, go back to basics. There is no two schools of thought on how you test for Ze at the origin, correct? There is "remove the earth conductor and measure directly onto that", and anything (other than something that achieves electrically exactly the same effect) else is simply wrong, correct? And if one understands why it is that way, then I find it difficult to see how one can fail to extend that principle more generally into one's testing wherever it is critical to be correct (EIC, EICR). I can understand why it's fine on a MWC where you just want a basic assurance. That's how I feel about it anyway.
But I challenge anyone to find where it says that it is perfectly OK to take and use a Zs measurement even if it incorporates parallel paths which are not any part of the by-design earthing arrangement for the item under test.
Then why give you a choice of (R1+R2) or R2 on the schedule of test results ?
It depends who you talk to in the industry, both sides gives pro's and cons.
The Ze measurement is slightly different, and even that may be obtained by enquiry, sometimes where it is not possible to power down for example a Zdb measurement may be used.
I take it you are fairly new to testing then ?, and/or limited to domestic ?
Obviously you would not design a circuit that relied on parallel paths, but sometimes on an EICR there are limitations as to how far you can T&I.
Don't understand the relevance, sorry?
In what way? The core point is exactly the same - avoidance of the influence of not-to-be-relied-upon parallel paths in a critical measurement.
Domestic and (on paper) small commercial. New to testing but have a certain amount of relevant experience from 20+ years of electrical and electronic engineering plus stuff in my own time. Was an MIEE before there was even an IET to be an M of :) Would still be only I resent paying their bloody annual fee. Got an Electrical & Electronic Engineering degree of 1991 vintage. Someone mentioning Norton and Thevenin has scared me by reminding me how much I've forgotten :)
You obviously don't understand what I am saying to you, if ever you test an industrial install that may have literally thousands of parallel paths you would understand.
Sometimes we are not permitted to power down, then we have to rely on either enquiry for the Ze, or a Zdb reading, in this case we would have to use a Zs measurement too, because calculated is not good enough to prove effective earthing exists, this would also include all parallel paths.
BS7671 allows us to record either (R1+R2) or R2 so long as we have a Zs measurement in the case of an R2 only measurement and the polarity is checked.
By using the (R1+R2) method we are checking the polarity at the same time, and we may also use a calculated Zs by adding the measured (R1+R2) to the measured Ze, this would not factor in any parallel paths, and this is my preferred method where possible.
Plus I like to include a measured Zs which may be lower than the calculated value, just to prove what value is actually present.
In the R2 method the measured Zs includes all of the parallel paths by default, and that is what is recorded.
Either method is acceptable, have a look at the schedule of test results in BS7671.
Both methods have their uses.
Spare 10 mins so just had a skim of GN3/OSG on the whole Zs saga to try and get some clarity around where I've got my understanding from. When you've been doing it a particular way you tend to forget why you do it that way!! Anyway salient points condensed as I interpret them:
Filling in of the 'Schedule of test results' (P100 GN3 -- for EICR or EIC) refers to using either of the methods on P52 for Zs.
P52 gives ......
1) 'Live' Zs is made with neither bonding or earth removed.
2) Zs can be a measured value or a calculated value.
OSG P162 also mentions test or measure for Zs .... why didnt I think of looking there earlier!
So everyones a winner and is right in the way they test, you've all passed the 2395(?) ........ if thats how you interpret the requirements of BS7671 :)
looking at the original post and some of the replies regarding the difference between the voltage used for the test ie very low and the operating voltage,230 and how this affects readings ie 230 wont "see" the odd 0.05 ohm but the tester will,well it's a bit like hunting down a fault isn't it? sometimes you don't find it with 230 but IR at 1000v and all is revealed.
(GN3) P52 gives ......
Yep, agree with that and GN3 actually states it is down to personal preference. And not a mention of parallel paths. In terms of what the books say, you're right. BS7671 seems to add nothing useful on the point. Well well. I have to admit to being pretty gobsmacked about them being apparently so relaxed about their implied suggestion of "just measure Zs if that suits your mood, don't worry about how much of the R2 is actually a parallel path through a boiler that's being ripped out next week".
Yebbut that's for an obviously physical reason of stuff breaking down at higher voltages (plus on my meter for example, on 250V IR test the reading hits end of range at 200Mohm; on higher ranges it's 1000Mohm so anything between 200 and 1000 will be picked up as a reading).
That is because you are thinking in terms of domestic with only a few circuits.
The second method is allowed because that may be the only way to test a larger install.
Think of even a small factory unit with all metal clad accessories installed in metallic conduit and metal trunking which may be fixed to the structural steel, there will be many parallel paths and it would be virtually impossible to try and remove them all just to carry out an EICR it is simply not practical.
On even larger complexes with metal pipework, metal ducting and machines etc. it would be nigh on impossible unless you were ripping the whole place apart.
.... "just measure Zs if that suits your mood, don't worry about how much of the R2 is actually a parallel path through a boiler that's being ripped out next week".
I think it boils down to you can't predict whats going to happen in the future, you can only play with the cards dealt to you now! Plus of course we all know people only use "competent/registered tradesmen" to do their work for them. And through their training and experience these tradesmen would clearly be appreciative of the problems they could cause .....
That is because you are thinking in terms of domestic with only a few circuits. The second method is allowed because that may be the only way to test a larger install.
No, I do understand that, absolutely; but my point is, why not clearly point out the parallel paths risk that comes with the direct Zs measurement rather than declare it to be a matter of personal taste? Something like "Measure Zs direct by all means if you must, but beware the parallel path Jabberwock, my son."
Because as a "competent person" you are supposed to know this, lol, GN3 and associated literature is only to guide you as far as the regs are concerned, it not meant to teach you how to T&I, only how to comply with the requirements of BS7671.
Reply to When Is 0.5ohms Not 0.5ohms? in the UK Electrical Forum area at ElectriciansForums.net