Take a step back and take another photo.
the lidless trunking bottom left?

as for the incomer, seems to be leaking.
 
It's probably fine in terms of integrity - the leaking may be an issue - not sure if this is the sort that has pitch in, if so it may indicate overheating.

With that and the seemingly broken screw, I'd be getting the DNO out to look at it and determine it's safety for continued use (or not)
 
Sorry it’s the only picture I have whilst working in the room this morning. Trunking lid was missing - no were to be seen. DNO to attend site tomorrow
 
I went to this one not so long ago!
IMG_20201119_0936398.jpg

Had the DNO out to this one although not leaking like yours! They said it was fine until I asked them to isolate it so I could put a main isolator in. Then all of a sudden it needed a new cut out! They were back a little while later in the month and put a new cut out in and fitted an isolator. So could go either way tomorrow!
 
I have this one to sort out at some point - single phase but same vintage I assume - it's on my list to get UKPN to look at.

Let us know what happens.

IMG_20210318_125638.jpg
 
I went to this one not so long ago!
What an utterly bizarre thing to do with the 'DNO earth' and a Henley block!

Why not a crimp lug under the same bolt that attached it to the case, and take that new cable to the 'MET' block?
 
Re the OP, I can't see clearly whether it is leaking pitch, which can be a sign of overheating (although it can very slowly ooze out of holes anyway). It appears to be leaking cable compound (the liquid impregnant of the paper insulation) which sometimes happens if the head is at a low point in the cable run and the compound is under hydrostatic pressure. This is not a sign of overheating but can indicate it's not properly sealed.

Don't forget that if you can get the DNO guys to leave them behind I can pay beer coupons for these because we need all kinds of DNO gear for the museum.
 
Cutout on job currently on, old but perfect Nick!
 

Attachments

  • 26466A65-47AD-4F0C-B53B-5B3935174BA5.jpeg
    26466A65-47AD-4F0C-B53B-5B3935174BA5.jpeg
    445.4 KB · Views: 91
@Peakyblinder89
Did you get a good outcome from the visit?
Or did they not attend like a job I have been on where they promised to come out and didn't bother? And yes it has got a bs951 earth clamp around the incoming cable!
IMG_20210604_1207331.jpg
 
@Peakyblinder89
Did you get a good outcome from the visit?
Or did they not attend like a job I have been on where they promised to come out and didn't bother? And yes it has got a bs951 earth clamp around the incoming cable!View attachment 87011
Interesting titbit about those clamps. There was a period (late 70s I think), when 951 clamps were specified as suitable for providing TN-S earthing. This came up on one of the E5 podcasts I believe - possibly one on coding for EICRs.

So it's possible that it was compliant when it was installed, and not just a bodge by someone later on - although that is of course a very real possibility...
 
@Dartlec that is interesting and I had not heard that before! Unfortunately in this case there was originally a proper sweated connection probably about the equivalent of 4mm, it looks to have been either deliberately cut off by the last electrician who was there or snapped off previously!
 
  • Like
Reactions: Dartlec
@Peakyblinder89
Did you get a good outcome from the visit?
Or did they not attend like a job I have been on where they promised to come out and didn't bother? And yes it has got a bs951 earth clamp around the incoming cable!View attachment 87011
Spoke to my client last thing today to see how they got on, she said shes still waiting to hear back from SP customer service, shes going to chase them again tomorrow
 
  • Like
Reactions: SparkySy
Interesting titbit about those clamps. There was a period (late 70s I think), when 951 clamps were specified as suitable for providing TN-S earthing. This came up on one of the E5 podcasts I believe - possibly one on coding for EICRs.

So it's possible that it was compliant when it was installed, and not just a bodge by someone later on - although that is of course a very real possibility...
I generally get the DNO out to get rid of the 951 clamp had it a few times when doing a Ze test where there was arcing at the clamp, the first time I found the problem I heard a noise when I pressed the test button tried it a second time and heard it again switched the cupboard light off and hit the test button again and saw the flash at the clamp. When the DNO removed the clamp you could actually see where it had arced on the clamp
 
Spoke to my client again this afternoon, still no response from SP customer service. She isn’t very happy
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Liverpool
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
PB89 Elec

Thread Information

Title
Main incomer
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
Peakyblinder89,
Last reply from
Peakyblinder89,
Replies
16
Views
4,645

Advert