table

  1. L

    R1+R2 Values

    Hi all, Quick question when doing r1+r2 testing wether its a new install or a EICR, is there a table to show maximum readings we should be getting? Or is it a calculation? Thanks in advance Luke
  2. S

    Assignment help

    Determine the minimum size of cpc for the circuit giving consideration to; Disconnection times Thermal Constraints? Here is what I have worked out so far for the circuit - Ib=p/(Ulx√3) = 12000/(400 x 1.732) = 17.32Amps From Table B6 I selected a C20 which has a max Zs of 0.87 Ω 20>17.32...
  3. Flanders

    4mm 90 Degree Thermosetting cable on a 32 amp MCB

    Hello Can I just confirm that if 90 degree cable is used in switch gear that is only ratted at 70 degrees then you use the 70 degree tables to find the maximum current carrying capacity in this case Table 4D1A I ask this as I carried out an EICR and found 4mm 6491B cable run in trunking...
  4. E

    Ci - for cable calcs

    Also just revising: trying to apply a rating factor for insulation on a cable calc. Just in theory, it's not for an actual job. The cable will be clipped direct to joists above ceiling and is covered in >100mm thermal insulation. I cannot find the correction factor for insulation. Advice please!
  5. A

    Max Zs table

    hi folks, does anyone have a copy or link to the most recent maz zs tables? ive only got green book and know they've been updated, was it 10% extra roughly. i used to have a link saved on my phone but i must have deleted it by mistake, thanks.
  6. D

    Derating Factors

    Hi guys, Might be a silly question but getting really confused. Table 4D5 for choosing cable size for different installation methods, does this already have de-rating factors applied for the different methods? If so, then if you calculated your current capacity using specific de-rating factors...
  7. KennyKen

    How do you get promoted to Electricians Arm status?

    Got a Gold J.I.B card if that helps?
  8. S

    Volt Drop table help

    Hi, I was calculating volt drop today using xlpe armoured cable, 3 core, single phase. Table 4E4A pg 373. I am using 3 core cable but on single phase, so i would assume column 3 for single phase. I was told by the tech helpline although the cable is being used for single phase that column 4...
  9. J

    Rewire a table lamp - any help appreciated!

    Hi, I have a table lamp that I love but it only allows bulbs up to 50 watt although the shade is large and open so not really a fire hazard. I have been using halogen bulbs to the equivalent of 70 watts (I think they're around 42 watt but I threw the box away) but they only last about a month...
  10. haptism

    Table 7.1 Osg

    Hi all hope all is well and nice layout for the forum, like it. Been flicking through the OSG and notice that in table 7.1 (max cable lengths for final circuits) that there are no cb's or rcbo's rated above 40A. Is this because they feel like no ones interested in anything above 40A, am i...
  11. M

    1NO1NC switch

    i am trying to install a 1no1nc push on off led switch in my car to intercept my power antennae. it has 5 terminals with red, white, black and 2 green wires. the 2 green wires are marked NO and NC. i think the red is marked+. cannot see any markings for black and white wires.it did not come...
  12. juice

    do you use the multipliers from tab 13 in OSG when calulating volt drop?

    I've recently done a C&G 2396 Electrical Design Course and unfortunately the tutor who taught the course did so for the first time and in my opinion didn't do a good job of teaching the material. I'm now doing my revision for an exam this Thursday and trying to make sure all the formula I use...
  13. A

    BS 7671 Table 41.3, conductor temperature?

    Edited: sorry of course Ze should be added to the post below, Table 41.3 is for comparing Zs. Hi, it is my understanding that Table 41.3 of BS 7671 should be used for comparing the tabulated values with the resistances of: 1) the line conductor at 70 degC; 2) cpc at initial temperature, as...
  14. S

    240v 1ph 1600W Table saw motor wiring question

    Hello everyone, This is my first post, so please bear with me. I am trying to work out how the motor to my table saw is wired. I bought it second hand and I think the previous owner has messed with it. One of the brush holders had been forced in and was touching the commutator. I am wondering...
  15. J

    On site guide single core Mv/A/m question

    Hello all I have a quick question on using my on site guide. I've found this forum fantastic for help so far. It's quite simple. I have a question which asks what the voltage drop for a single core 6mm² 70⁰c insulted cable for a single phase circuit is, enclosed in conduit. Page 151 of the...
  16. happysteve

    Another OSG error I haven't seen mentioned... RCD and zones

    Eh up :) We all know about the duff max Zs tables in the OSG (Table B6) and GN3 (Table A4)... in fact, I've only just recently updated my GN3, and I'm pleased to say they have reprinted it and it now has the correct tables in. I've noticed in my (early-purchased, with dodgy table B6) OSG that...
  17. 1capybara

    Table 41.3 Max earth fault loop impedence (Zs)

    The heading of table 41.3 says it shows " max earth fault loop impedance Zs for Circuits Breakers..... giving compliance with 0.4s disconnnect time of 411.3.2.2 and 5s disconnnect time of 411.3.2.3." 411.3.2.2 is for final circuits not exceeding 32A. 411.3.2.3 is for distribution circuits and...
  18. driverman

    BSEN 12464-2:2007 table 5.4 item 5.4.2

    Hi guys, as title suggest re spec for some lights. At this point in time I've not got a scooby doo what it's all about. any pointers, links. I will try google later.
  19. HappyHippyDad

    Is there a table of expected R1+R2 results in BS7671?

    Evening... I always use my OSG to find R1+R2 when needed for designing a circuit (staying withing the Zs limits), but I wondered if the same table is somewhere in BS7671? Its table I1 in the OSG. I've hunted high and low so I expect it's just something that the OSG offers and isn't in BS7671...
  20. A

    Max permissible ZS for rcbo 61009

    So, when I did my 2391 I&t course I was told to use to values in table 41.3 of the regs for max ZS value for rcbo which provide earth fault, and over load protection. Recently a colleague of mine said you should use the value in table 41.5 which states a max permissible ZS of 1667 ohms. I don't...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock