Evening..
I have completed EICR and discovered an issue with the ring.
The ring serves the whole house. A previous report from 2 years ago had it down as broken and they changed the 32A mcb for a 20A mcb. The client new this and has rightly asked for the fault to be found.
When I tested the ring at the CU r1, r2 and rn were all adequate (r1=0.31, r2=0.72, rn=0.32). However, at the vast majority of sockets r1, r2 and rn were all showing >1999ohms.
I did start writing out my ideas but I've just deleted it as they sounded poor and I have to get the boy to bed!
Something along the line of a very long radial off one of the sockets!!??
Any thoughts welcome.
I have completed EICR and discovered an issue with the ring.
The ring serves the whole house. A previous report from 2 years ago had it down as broken and they changed the 32A mcb for a 20A mcb. The client new this and has rightly asked for the fault to be found.
When I tested the ring at the CU r1, r2 and rn were all adequate (r1=0.31, r2=0.72, rn=0.32). However, at the vast majority of sockets r1, r2 and rn were all showing >1999ohms.
I did start writing out my ideas but I've just deleted it as they sounded poor and I have to get the boy to bed!
Something along the line of a very long radial off one of the sockets!!??
Any thoughts welcome.