Gone to a job this morning had a call from a customer when i plug too much I'n on this side of the kitchen it trips the whole house, house DB protected by 30ma rcd. Went to the job apparently this has been the case for 4 years or more. Happens then washing machine is on and toaster and kettle is used. Trip it now appears that 2x sockets on one side are on the ring. Over the other side on t&e goes down the wall to feed a socket above worktop, spur from this to under cuPboard lights, spur to socket below worktop to wm outlet, spur from this to tumble dryer, spur from this to double socket on worktop further over. Bingo! Problem solved overloading one t&e radial, from ringmain, must be jb above ceiling! All faceplates nackered a right mess under cupboards t&e lashed everywhere and you should only spur off once I've said best option is to run a new circuit. All old stranded cable however insulation resistance tests all good etc. Just to sort it all properly. It will take me a day on my own to complete and test, dabbing new ring into existing board surface trunk above units then drop behind units for 5 double sockets and 3 spurs for appliances. Was going to go I'n at 400 pounds does this sound fair ?
 
So the rcd is tripping the whole house, and IR are ok? sounds like some appliances are leaking current, the fixed wiring although a mess has returned satisfactory results.
 
sounds a fair price. only suggestion is might it be easier to run 2 radials, 1 to each side of the kitchen. use 4mm for the heavily loaded side at 32A and 2.5mm at 16A for the other side.
 
Gone to a job this morning had a call from a customer when i plug too much I'n on this side of the kitchen it trips the whole house, house DB protected by 30ma rcd. Went to the job apparently this has been the case for 4 years or more. Happens then washing machine is on and toaster and kettle is used. Trip it now appears that 2x sockets on one side are on the ring. Over the other side on t&e goes down the wall to feed a socket above worktop, spur from this to under cuPboard lights, spur to socket below worktop to wm outlet, spur from this to tumble dryer, spur from this to double socket on worktop further over. Bingo! Problem solved overloading one t&e radial, from ringmain, must be jb above ceiling! All faceplates nackered a right mess under cupboards t&e lashed everywhere and you should only spur off once I've said best option is to run a new circuit. All old stranded cable however insulation resistance tests all good etc. Just to sort it all properly. It will take me a day on my own to complete and test, dabbing new ring into existing board surface trunk above units then drop behind units for 5 double sockets and 3 spurs for appliances. Was going to go I'n at 400 pounds does this sound fair ?

Will this new circuit be protected by the single consumer unit RCD?
 
cause for tripping i came up with was OVERLOAD and yes carried out a full test on circuit and came up trumps. one side of kitchen 0.07, 0.06, and 0.04/5 readings on r1+r2 readings, over the other side where a visuall confirmed, a spur from ceiling for double socket on counter to another undercounter and a spur spur and one final double socket, leg came up through boxing and fed another double further alond the counter.

OVERLOAD? max amperage for one 2.5mm cable approx 21a at best?? and if you plug in kettle whilst washing machine is going??
 
non rcd fuseboard, hager, all MCB'S protected by a seperate 30MA RCD thats been added at some point of the installations life. so this enables all MCB's to now be 30Ma protected.
 
r1+r2 readings over other side were 0.24, 0.28, 0.32, 0.44 at last point (double socket) confirms its a radial (spur off spur off spur)

my cause for concern as to why its tripping RCD unit. OVERLOAD! especally as its a spur off a spur off a spur etc.
 
being a numpty. hob was original cause for 30Ma RCD to trip whole house! i dissconnected that.

My secondry problem was indeed MCB tripping Kitchen ring, when 2 or more appliances were plugged in over one side! however this fault is the intermittent one over past four years. Make sense now?
 
being a numpty. hob was original cause for 30Ma RCD to trip whole house! i dissconnected that.

My secondry problem was indeed MCB tripping Kitchen ring, when 2 or more appliances were plugged in over one side! however this fault is the intermittent one over past four years. Make sense now?

Yes now we have the full picture, what size mcb was it?
 
ok lets think about this, so if you rewire into a ring, and plug these appliances in, do you think it will stop tripping the 32 amp 'b; breaker?
 
MCB tripping as 2.5 spured from ring feeds, 2 or more appliances, kettle toaster w/m, one single 2.5 max 27a depending on installation methords so at best, so this side of kitchen is clearly overloaded?? thats my logic?
 
lets not get confused with cable ratings for the minute, as you have done an IR test, the cable has stood the test of the current of these machines, I trust you got >200M
 
let me explain, cooker 6mm radial, 32 type b MCB, Hager.

from cooker switch oven is connected to outlet, from outlet a s/so with hob plugged in (plugtop) this is what was tripping, RCD, knocking out all power to DB. dissconnected that. problem solved. he told me, was a bit silly cleaning it soaked it and hadnt worked since then. (TRIP)



APPLIANCES on KITCHEN RING, toaster, kettle, t/d, w/m, fridge.

when too much is plugged in over the "spured side" thats when MCB tripps
 
ok, if you change the circuit to a ring, you will still have the same amount of current flowing through the MCB, regardless of spurs etc, with everything plugged in, so the MCB will still trip.
 
Look up Kirchoff current laws, it is very interesting, and one of the first principles that I learnt at college.

God knows what they teach these kids nowadays
 
is the most probable cause to all this was because the spurred 2.5mm leg was overloaded at times causing MCB too trip? this logic IS possible?

i just didnt want to rewire and the same problem to occur! how silly would I look!

i just want too make sure there was logic in my conclusion!
 
Can you run a new cable 4mm to feed half the overloaded side on a 32 amp mcb
The existing 2 feeds will become 2x20amp radials

Ending up with 2x20amp radials and one 32 amp radial
Spreading that load should help rather than trying to solve it by using rings
 

Reply to Advice suggestions please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
472
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
516
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
315
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
680
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock