[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]Getting a bit of a headache here, hoping someone can break this down for me please.

Are there any instances where table 41.3 of BS7671 do not apply, and table 41.5 will instead apply? [/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]
[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]Example[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]
[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]32A type C RCBO having a max Zs of 0.58 (after RoT applied).[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]Measures value of Zs coming in at 1.14.[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]Ring circuit. [/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]
[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]To me: Doesn't comply and the RCBO should be changed to a type B, having a max Zs after RoT of 1.16.[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]
[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]What I am told:[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]A mixture of something about the max Zs being different with an RCBO as oppose a CB (MCB). [/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]Me: Well that doesn't make sense as table 41.3 references RCBO's as well as CB's. [/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]
[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]Because the circuit is protected by an RCD, as long as the Measures Zs is under the value stated in table 41.5 which holds a value of 1667 ohms for a 30mA RCD then it's all fine. [/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]Me: Well that just seems daft. [/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]
[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]As I understand it, if there is an over current on the circuit, the CB will not trip in under 0.4 seconds as the Zs is too high, and the RCD referred to in table 41.5 which is protecting the circuit from an earth fault doesn't react to an over current. [/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]
[/FONT]
[FONT=Verdana, Arial, Tahoma, Calibri, Geneva, sans-serif]Or am I missing something obvious here?


[/FONT]

 
Ok,

The RCD part of the RCBO is providing additional protection, Although in reality the RCD part will trip under earth fault conditions before the MCB; but as it's a TN system then the Max Zs is 0.58 ohms.

If the earthing arrangement was TT then this would be different. You could then use the 1667 ohms because of "Ra x I delta n <= 50 V.


 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
BSEN 7671 Table 41.5
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
3

Thread Tags

Tags Tags
table

Advert

Thread statistics

Created
SDH,
Last reply from
Simonslimline,
Replies
3
Views
124

Advert