jonney88

I know u just put it down as a code 3 but do u put down ads or eebads or is it always ads now??
 
not sure yet im going to the job Monday all I know is its a dental surgery, with no rcd protection an any circuit gas is bonded and so is water,,need to check special locations yet as to if its classed as a medical location,, but because its not to current regs either ensure cross bonding is done and use eebads or upgrade to rcbos and its covered but just thinking of cost as thers about 8-9 db's
 
If it's ADS put down ADS, if not, put down whatever type of protective measure is utilised?!

Not really sure what RCDs have to do with anything?
 
  • Like
Reactions: 1 person
well I thought your methods of fault protection were eebads if thers no rcd protection,, and ads no rcd protection if its fully contained exept for socket outlet or if its monitored by a competent person
 
are you Zs readings compliant with BS7671 disconnection times for each circuit? if so you just give the lack of RCD protection a code C3, unless the use of any sockets ( e.g. outdoors ) warrants a code C2, or if there's no supp. bonding in special locations ( also a C2).
 
well I thought your methods of fault protection were eebads if thers no rcd protection,, and ads no rcd protection if its fully contained exept for socket outlet or if its monitored by a competent person

I think you need to read up on section 41
 
its my dads business, I want to do wats right and least costly but it im, see all I usually do is report back recommendations to the office, and they take it from ther but this is a good opportunity for me to delv alittle deaper into the regs and learn something aswell,,eeb earth equipitential bonding,,, lol yes is got it wen u said I I automaticly assumed cross bonding, which because I trained to the 17th and im mainly on new install don't really come across it
 
Hehe, got you :)
I note you're concerned about cost but have you seen how much those buggers charge?
Probably not because your dad fixes your teeth
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
eicr on premsis with no rcd
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
jonney88,
Last reply from
trev,
Replies
9
Views
2,007

Advert