mtfpuk2011

Can someone please help with the following exam question revision. Have seen the same question twice now on two different exam papers and each answer supplied by them have been different. I am confused.

A radial socket outlet is supplied by a 2.5mm2/1.5mm2 cable that is 20m long. Given that the Ze of the installation is 0.43Ohms and the resitivity of the cable is 7.41mOhms/m/12.1mOhms/m at 20 deg C, what is the calculated Zs taking into account of operating temperature?

a 0.892 Ohms
b 0.8283 Ohms
c 0.3932 Ohms
d 1.2 Ohms

The first paper gave the answer as D. 1.2 Ohms, the second paper, A. 0.892 Ohms. I have figured out ways of getting both answers but don't know now which answer is right! Exam is tomorrow.

Thanks
 
What is the operating temperature of the cable! I would guess that some information is missing from the question! I would calculate it this way 12.1 + 7.41 = 19.51 m ohms /m multiplied by 20 meters. 19.51 x 20 = 390.2 m ohms /m. Divide that by 1000 to bring it back to ohms. 390.2/1000 = 0.390 ohms. I would then multiply that by 1.2 to bring it up to 70 degrees as copper resistance will increase by 2% for each 5 degrees.(If that info was in the question ) 0.390 x 1.2 = 0.468 and then add the ZE of 0.430 = 0.898 ohms so even my answer is not on your list !
 
What is the operating temperature of the cable! I would guess that some information is missing from the question! I would calculate it this way 12.1 + 7.41 = 19.51 m ohms /m multiplied by 20 meters. 19.51 x 20 = 390.2 m ohms /m. Divide that by 1000 to bring it back to ohms. 390.2/1000 = 0.390 ohms. I would then multiply that by 1.2 to bring it up to 70 degrees as copper resistance will increase by 2% for each 5 degrees.(If that info was in the question ) 0.390 x 1.2 = 0.468 and then add the ZE of 0.430 = 0.898 ohms so even my answer is not on your list !

I am sooo sorry. Your answer must be correct. I had missed out a digit on answer a which is 0.8982 Ohms.

Thank you. That clairifes it. Don't why the other paper worked it out to be 1.2 Ohms though. You can see my confusion! Thanks for explaining it so clearly
 
What is the operating temperature of the cable! I would guess that some information is missing from the question! I would calculate it this way 12.1 + 7.41 = 19.51 m ohms /m multiplied by 20 meters. 19.51 x 20 = 390.2 m ohms /m. Divide that by 1000 to bring it back to ohms. 390.2/1000 = 0.390 ohms. I would then multiply that by 1.2 to bring it up to 70 degrees as copper resistance will increase by 2% for each 5 degrees.(If that info was in the question ) 0.390 x 1.2 = 0.468 and then add the ZE of 0.430 = 0.898 ohms so even my answer is not on your list !

I got the same answer

R1R2LFZeR1 + R2 x L/1000R1 + R2 x L/1000 x FZs Design
7.4112.12010001.20.430.39020.468240.858
 
Thank you again. Is the correction factor of 1.2 always used or only at temperatures of 20 deg. C?

You need to look in your GN3 & OSG, explanation will be much better!
Basically, as temp rises, resistance rises, so you need to correct. See above references.

The 1.2 is the adjustment from 20 to 70degC
 
Thank you again. Is the correction factor of 1.2 always used or only at temperatures of 20 deg. C?

F it is always 1.2 (PVC 70 Celsius bunched see table I3 OSG) when calculating Design Zs, if you use either r1 r2 values from OSG or GN3, if using LSF cable or MICC different correction Factor.
Only if installation is a specialist with either higher or lower temp would you need to use Table I2 (boilers houses would have an ambient say 40 Celsius) green house could be say 0 Celsius to 35 Celsius ambient. You would told this in an exam question. In the practical world if you were testing and installation and you need to wear extra clothing is probably lower then 20 Celsius, like wise if your sweating it greater then 20 Celsius. I used a digital thermometer similar to try you see in fridges, for measuring commercial fridge temperature.
So for your exam F will always be 1.2 (70 C PVC)
 

Reply to Exam revision calculation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K
signed up to 247 training uk with payments associated with Carnegie Consumer Finance paying £180 per month. I did 9/39 models to do the pre...
Replies
10
Views
4K
SORRY FOR LONG POST. So i have my 2391-52 multiple questions coming up on Friday 13th, ( yeh i know) and was giving some things to study over by...
Replies
4
Views
2K
Hi, I have an engineer who is completing his 2391-52 exam tonight and he has been told one of his mock questions was wrong, I have completed the...
Replies
19
Views
5K
Afternoon all, How do i solve these two questions, Feel like am missing something simple. doing my head in lol. I need to learn the calculation...
Replies
24
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock