Hi I have a house where in order for the rising main to be earthed, the earth goes around the outside of the property to the fuse box in 10mm cable clipped to the wall at damp proof level. It has no conduit protection. I have recently asked an electrician to upgrade the fuse box and he suggests that the earth is non compliant it is not protected.

Is this the case and what should the cable be protected by?- solid or corrugated trunking?

Any thoughts would be welcome
 
Well I'd personally mechanically protect it if I'd installed it however bs 7671 gives a minimum CSA of 4mm where mechanical protection is not needed for applications such as supplementary bonding and earthing where the conductor is not part of a cable or mechanically protected.
maybe he means the main earthing conductor should be 16mm? Or is the 10mm for the gas or water?
 
It is also prone to solar damage.
 
It is almost certainly not non compliant but it could be improved. There are many millions of cables installed in this manner. It could most easily be enclosed in conduit though getting the end of the cable available may be inconvenient.
 
  • Agree
Reactions: suffolkspark
Hi I have a house where in order for the rising main to be earthed, the earth goes around the outside of the property to the fuse box in 10mm cable clipped to the wall at damp proof level. It has no conduit protection. I have recently asked an electrician to upgrade the fuse box and he suggests that the earth is non compliant it is not protected.

Is this the case and what should the cable be protected by?- solid or corrugated trunking?

Any thoughts would be welcome
I would also be concerned about a possible bridge of the DPC
 
Think meeces like green and green & yellow cables.
 
It's not UV tolerant so should ideally be covered. After 10years or so of being battered by the sun the insulation will go brittle and crack etc.
 
  • Agree
Reactions: westward10
If its a substatial cable - Metal theives are of concern.
( in an exposed state it is being regularily inspected !)
 
Last edited:
  • Like
Reactions: Rpa07
ideal would be to enclose in black pvc conduit. to do this obviously, to thread it through, entails disconnecting one end. this should be done (in an ideal world) with the installation isolated from supply.
 
  • Like
Reactions: Pete999
or just cut it half way, thread tube (and elbows) over both halves of cable, fit through box, add saddles/clips, crimp joint cable in through box. 30 minutes - done.
 
Unplasticiced polyvinyl chloride.
Does not decompose or change colour/rot in sunlight.
Google it!
 
In another place not governed by BS7671 practice was to paint over exposed cable if it was on a painted surface to slow the UV attack. Wilko rates a good slather of plastic paint SPF 100 :) .
 
  • Funny
Reactions: Rpa07
that plastic paint is cheap. it has to be for all these female models and celebs to trowel it on their faces.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
shrewsbury

Thread Information

Title
External Earth Cable Protection
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
SteveSmallholder,
Last reply from
telectrix,
Replies
19
Views
15,364

Advert