Discuss FAULT FINDING in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Eire79
ok, iv a domestic house with a shed 50 mtrs away supplied via 3x10 SWA on a B32A MCB. fault has been occurring the last few days which is the MCB in house tripping.
I arrive and open both boards and remove both PE and N conductors from terminals followed by IR testing and was getting very poor results between all conductors, then just out of interest i powered back up with phase only and main switch in shed isolated plus PE and N still removed .
I was recording voltage of 230v from the disconnected PE to the MET at the house and 180v between the PE and N conductor supposedly dead legs therefore i was expecting a trip again when i connected back up all conductors but no , nothing happened.
I am pretty confidant that the SWA is damaged but why is it not tripping constantly, is it a high resistance fault thereby not enough fault current flowing.
I also carried out fault loop at the house and shed which were .15 ohms and .33ohms.
Looking forward to your opinion's.
If you just used a multimeter or similar you could easily see that sort of voltage just from the cable capacitance.
When you say very poor IR what values did you see for L - N&E and from N - E? (presumably cable only, with the shed disconnected)
Did you also IR the shed to see if something at fault there? Water or small creatures getting in to socket boxes, etc, springs to mind...
If you think the SWA is damaged, what are the IR test results (measured at 500V) for the cable, disconnected both ends: L to N, L to E, N to E, and then each in turn of L, N and E to the armour (I've assumed this is a 3-core cable).
IR results were in the region of 30 to 50 M ohms, that was on everything at 500v and even at 250v the results were poor. I think your correct with cable damage or maybe a joint underground not correctly terminated. either way a new cable is required now.
No I used the multifunction to check voltage.IR was 30 to 50 M ohms with both ends disconnected. I understand what you mean with capacitance, I came across a fault once in a industrial premises where a spark installed a metalclad RCD socket that would not trip, when I checked voltage to earth it was 230 until a load was plugged in resulting in the 230v to earth disappearing.
That's why I keep telling lads to test everything.
[automerge]1591636370[/automerge]
Unless there is an intermittent fault the insulation test is failing to break down then in my eyes 30-50 Mohm is not an issue.
Sorry all I mean 3 to 5 M
[automerge]1591636547[/automerge]
Sorry all its 3 to 5 M ohms , although its been very dry lately so I'm baffled as to tripping issue , id say something if it was raining
so it's not an earth leakage fault. it's an overload or a short circuit. could even be a duff MCB.
It doesn't often happen, but I replaced a faulty MCB recently: it had been poorly-terminated to the bus bar, which had over time caused thermal damage (visible discolouring), which led to occasional tripping. Even the physical switch mechanism had been affected though, and the bus bar terminal was very tight and gritty to unscrew.
Update, mcb still tripping so got meters out again and this time 980 ohms between phase and earth so cable damaged . Bit of a awkward job ahead now getting a new cable out.
Reply to FAULT FINDING in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Hi I'm trying to find if I have a fault in these to brakers of in the lines. The 32A braker leads as far as I know only to a junction box that use...
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...