Hi there,

If I’ve got a SWA, what size should my fly lead cable be from banjo to earth bar ? The wire armouring is only being used for mechanical protection and not by means of supplying a earth.

If I am using the SWA as means of a earth connection how do I size the fly lead then?
 
I would also tend to make it CPC-size, whether the only CPC or in parallel with a copper CPC. One could argue that if the armour is only serving to protect the cable and is not connected to anything downstream (e.g. the far end is TT) it only needs to provide for the short-circuit requirements and could be sized adiabatically. However it most situations the saving would be trivial so I would tend to ignore this option.
 
On the subject of earthing the swa been to a job today where they have extended a ring to a small outhouse using a wiska box that is too small to use the banjo and locking nuts inside.....any tips on earthing the armoured without having to take it all apart and replace the box
 
Agree with the above: the flying lead should be able to take out the supplying OCPD in the event of an internal cable fault so probably no less than half the phase conductor CSA as a rule-of-thumb.
 
Thinking about the above, the steel wire has a given factor which can be read on a chart I have seen here several times. I understand the SWA of the cable has a factor of 8 times to consider when using as an earth. If you match the CPC of the SWA surely the flylead would have a higher fault current tolerance than the SWA of the the cable?
 
Thinking about the above, the steel wire has a given factor which can be read on a chart I have seen here several times. I understand the SWA of the cable has a factor of 8 times to consider when using as an earth. If you match the CPC of the SWA surely the flylead would have a higher fault current tolerance than the SWA of the the cable?
I suspect @Dustydazzler was referring to the CPC size of the supplying circuit (e.g. if fed from from 4mm T&E then 2.5mm CPC, etc)

Generally for smaller SWA sizes the CPC is fine, but there comes a point when the armour is no longer able to cope with the adiabatic stress due to the higher resistance of the steel.
 
If in doubt use the adiabatic equation to work out the required cpc size. Depending on size if a 3C or 4C is used you will need a nominal sized green & yellow to tie the armour down to earth!
 
Thinking about the above, the steel wire has a given factor which can be read on a chart I have seen here several times. I understand the SWA of the cable has a factor of 8 times to consider when using as an earth. If you match the CPC of the SWA surely the flylead would have a higher fault current tolerance than the SWA of the the cable?

The 8 times conductivity is used as a factor when assessing the Armour as a bonding conductor rather than its use as a cpc.
 
Prysmian has a useful table at the back of the data sheet listing resistance and CSA of the armour (for adiabatic test), but I suspect these are the DC terms as it is slightly less than the AC volt drop equivalent:


Somewhere I remember seeing a table that was a quick yes/no to armour as CPC limits

As @timbobelfast has already said you can run a copper CPC external to the SWA cable, subject to it being mechanically safe (e.g. in a duct, etc) if you can't get, or afford, SWA with an internal copper conductor used as CPC. After all 5-core is well over 20% more expensive than 4-core, and often the supplementary CPC need only be half the phase size.
 

Reply to Fly Lead Size to SWA in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
Replies
7
Views
1K
resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
Replies
1
Views
1K
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K
Hi all. Could I ask some advice please regarding SWA banjo fly lead sizing. Can anyone explain what sizing or how you size the required earth...
Replies
6
Views
3K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock