So I’m installling a garage DB 63a 30ma RCD
With. 6a and 32a mcb Using 2.5 swa from the consumer unit what would the rated needed for protection on the house DB?
 
Last edited by a moderator:
is the 2.5mm SWA alreadyinstalled?or are you installing it?
 
Yeah is currently a spurred cable off a ring 32a mcb in the DB than 2.5 to the spurred fused switch then the swa running to the garage the a nother fused switch with a spurred double socket and a single light and switch
[automerge]1580759074[/automerge]
Sorry mA, pig ---- for fingers
 
in that case it'd poor practice to fit a sub main in the garage. you're stuck with what you have.
 
In that case I was going to give it its own 20a mcb in the DB??
 
If it's currently fed off a ring through an FCU whats the issue? If you are only running a 2.5mm SWA then there cant be a lot of load??
 
No but wanted to increase to 3 double sockets on radial and a addition lamp
 
No but wanted to increase to 3 double sockets on radial and a addition lamp

Nothing to stop you adding as many sockets as you want, maximum load will be 13a but generally that's ample capacity for a garage, unless you have a couple of freezers and a tumble dryer for example
 
Ok cool no only one little chest freezer! Think I need to sort this first
[automerge]1580761543[/automerge]
6964710E-DFEF-46DB-96FA-E0AE84310F0F.jpeg
 
Yes, unlikely any RCD protection to existing sockets/circuits!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bristol
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Garage installation
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Robc77,
Last reply from
DefyG,
Replies
9
Views
1,773

Advert