That makes sense now mainline!
 
  • Like
Reactions: mainline
Clueless householder here!

My wife told me John Lewis refused to plug in our new oven this morning due to "high readings on sockets". It looks on their paperwork like the "Pre Earth Loop Impedance Test" failed with 2.02 Ohms.

I thought that was strange as we had a new consumer unit fitted and tested after buying the house, so I dug out the installation certificate which apparently says under part 5: "Supply company should be contacted to correct the very High Ze Reading of 1.57 Ohms without delay". Who knew? It says it's a TNS supply.

So not exactly without delay I decided to call 105 (SSEN) and apparently they'll send someone out. What should I expect from them?

Pretty sure I can figure out plugging in an oven myself but if this is dangerous I'd like to get it sorted.

View attachment 117902

View attachment 117903

View attachment 117904
this is very old and I would have it ripped out and replaced, the Provider sse will probably say it needs stripping out and get things moving for you hopefully. Been a while since I saw anything this age, around here most places I have been it are in better nick, that was once though a great job installed by a decent guy and over the years aged and somehow the main earth has ended up like a pigs ear.
 
  • Like
Reactions: samtheman
Is the wall with the cut out and gas meter on an outside wall with access outside?

I suspect if SSE decide to replace the head they'll want to dig up outside and joint the cable and then fit the new head in an external box, or if no space come through to inside with a new cable and fit the new cutout away from the gas meter.

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
England
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
High Ze TNS - what to expect from DNO?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Thread Tags

Advert

Thread statistics

Created
samtheman,
Last reply from
samtheman,
Replies
22
Views
2,269

Advert