Hi everyone. Can anyone tell me the ip rating of a distribution board a) accessible top surface(horizontal) b) an intermediate barrier c) the vertical surfaces. Cheers
 
At least I got the reg right lol and that is only becasue this morning we were trying to get some boxes and I had it fresh in the mind ...........cheeers mate for the pull up
 
on this subject, can someone please tell me what the X 's refer to. i have always used IP44, IP66 etc.
 
I googled this because I couldn't remember (and don't have the regs with me at work (I work in IT Support at the mo) and found this on Voltium's Site:

Firstly, what does IPxxB mean, and secondly where is an 'appropriate' place for an electrical enclosure (lowbay) to be installed when it is only IP1x when suspended (i.e. has large holes <40mm on the back of it)? This is relating to 713-07-01 of BS7671. Can this fitting be installed as expected (trunk mounted 4-5m high) with the large holes open, and still comply? Thanks for any help,


starline.gif


IP code for ingress protection are given in BS EN 60529:1991 which is a standard used to form the basic requirements of electrical equipment standards. The degree of protection provided by an enclosure is indicated generally by two numbers and followed by an optional ltter oand or optional supplementary letter e.g IP 44 B H
The first numeral indicates the level of protection against ingress of solid foriegn bodies and protection against access to hazardous parts inside an enclosure.The 2nd numeral refers to the level of protection against ingress of water.If not required the numeral can be replace by X or XX.The additional letter indicates the degree of protection of persons against access to hazardous parts. It is only used if the protection against access to hazardous parts is higher than that indicated by the 1st character, or if only the protection against access to hazardous parts, and not general ingress is indicated, the 1st character numeral being replaced by X. The letter B - is protection against access with a finger (minimum 12mm diameter test finger, 80mm long) (Adeqauet clearance from live parts.

IP1X - is genrally protection against access to hazardous parts with the back of the hand and protection against foriegn solid objects of 50mm diameter and greater
regulation 713-07-01 requires that the verifier ensures the specified level of protection against direct contact is achieved - use the above as guidance i.e if the dsigner has specified xxB - you should not be able to stick a finger into the equipment and touch live parts and if IP1X is specified then as long as openings are less than 50mm this is satisfied.
If the fitting cannot be installed with this level of protection - the deigner should be consulted to either review the equipment specified or to assess the risks if using the type specified and to ensure safety.
I hope this is of help
Regards
Bob

The link is as follows:

Subcategory - 1. BS7671 - Voltimum UK - Electrical Installation Products and Contracting
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
IP ratings
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
wolfie1979,
Last reply from
malcolmsanford,
Replies
10
Views
11,228

Advert