Octopus

So who does these and why?

This has been passed to me for my comments by a customer:

Dander Notice.png


The "issue" is lack of end to end continuity of one of the socket circuits - I don't think this is a sensible use of a danger notice.

Do you?
 
I issue danger notices sometimes, I did one last week.
I usually reserve them for issues that would attract a C1 on an inspection where no immediate rectification is possible for whatever reason.

Just looked and I have 12 danger notifications in my files. 11 of them are for access to live parts less than IP2X without the use of a tool or key, and one is for a lack of main earth to a property where the customer was insistent I could crack on and install the wall lights he wanted. I issued that one to provoke a bit of thought.

The one in the OP should never have been a danger notice.
 
The last time I used one of them is when the cut-out was hanging off the wall, water had penetrated the consumer units, wiring was burnt out, verdigree on terminals, old cloth covered tails soaking wet, IR readings of <1 Mohm, Consumer units rotted away (old wylex), exposed live parts, main fuse had blown (replaced by DNO), no lighting, difficult access (cellar with no stairs)...need I go on?
 
The last time I used one of them is when the cut-out was hanging off the wall, water had penetrated the consumer units, wiring was burnt out, verdigree on terminals, old cloth covered tails soaking wet, IR readings of <1 Mohm, Consumer units rotted away (old wylex), exposed live parts, main fuse had blown (replaced by DNO), no lighting, difficult access (cellar with no stairs)...need I go on?

Nothing too serious then.
 
Am I right in thinking firstly that these notices need to be signed by the customer ?
I personally see no situation where these notices serve any purpose,I suspect they probably would not be acceptable for any legal proceedings

I honestly see no purpose at all in issuing these notices
 
Very seldom.

In the past year or so two that I can think of.

One Electrical Danger Notification for exposed live parts at a DB that they were adamant that they would rectify themselves. (Once the Danger Notification came through the door I had another phonecall asking what they needed to do to rectify it - which proved my belief that they had no sense of urgency about it before.)

And one Notice of Potential Hazard (the equivalent notice in the south of Ireland) when the incoming neutral tail was switched through the MCB for the immersion heater and the entire return path for the installation was through the Main Protective Conductor (which was also undersized) to the DSO's PEN conductor. It was established that this had been done to bypass the ESB meter. Although a rented premises, there was a distinct lack of urgency in addressing it.
 
I do one now and then. The last was for "Potential danger" in a rented property on TT without up-front RCD and ~ 100 Ohm Ra. It was the nicest way I could put it since the tenants were running about oblivious. Without it I suspect nothing would have happened. (Maybe it still hasn't).
 
QUOTE - [ I honestly see no purpose at all in issuing these notices ].
what about avoiding legal liability issue's ?
If your concerned about a certain danger
you advise the customer, customer says no
for what ever reason, maybe no money ?
If you issue a notice, then the ball is in there court
should something happen down the track.
sound logical to me
Have I missed some thing ?
 
The last time I used one of them is when the cut-out was hanging off the wall, water had penetrated the consumer units, wiring was burnt out, verdigree on terminals, old cloth covered tails soaking wet, IR readings of <1 Mohm, Consumer units rotted away (old wylex), exposed live parts, main fuse had blown (replaced by DNO), no lighting, difficult access (cellar with no stairs)...need I go on?

Up here the DNO (Scottish Power) would refuse to reconnect the supply without a certificate from an electrician saying the install was tested and OK.
 
I use these occasionally (2/3 in past year). I may use more than most as I do a lot of inspection and testing for 'skint' landlords.
It covers my back and places the liability on the client / landlord where there are exposed live parts.

Was at one on Friday to connect a cooker where the consumer unit had blanks missing - new tenants from down south who were unaware that the landlord had to install mains smoke detectors (not done) and provide a satisfactory electrical cert (also not done)
 

Reply to Issueing "danger notices" in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
269
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
551
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
756
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
We have had RG11 installed in some flats for use with Virgin/Internet. It should I think have been RG6 but the guy at Virgin was insistent it...
Replies
4
Views
381

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock