Just to Add, I have a 1552 and testing a circuit prior to a new board change had a loop on a ring circuit of 0.53.
After swapping the board and carrying out my test, I tested the same socket and got a reading of 1.03ohms. I called megger and after reporting the issue a very knowledgeable gent got back to me and said this seemed to occure when certain Manufacturers RCD's were installed (something to do with the coil size and greater resistance). I swapped the board out again from the Hager board to an MK board just to see if this was correct and sure enough I got a reading on that socket of 0.58 which was near enough for me! Anyone else had this issue ?
 
Just to Add, I have a 1552 and testing a circuit prior to a new board change had a loop on a ring circuit of 0.53.
After swapping the board and carrying out my test, I tested the same socket and got a reading of 1.03ohms. I called megger and after reporting the issue a very knowledgeable gent got back to me and said this seemed to occure when certain Manufacturers RCD's were installed (something to do with the coil size and greater resistance). I swapped the board out again from the Hager board to an MK board just to see if this was correct and sure enough I got a reading on that socket of 0.58 which was near enough for me! Anyone else had this issue ?


Yes.
Different devices can create different levels of impedance. This is one of the arguments against the NICEIC's new strategy saying would should only calculate Zs values for circuits where working live would be required in order to take a measurement.
 
Yes.
Different devices can create different levels of impedance. This is one of the arguments against the NICEIC's new strategy saying would should only calculate Zs values for circuits where working live would be required in order to take a measurement.

Spot on Widdler that was an argument I had with NICEIC a while back when he told a guy I know that Zs should not be done live but by calculation.

I was taught and now do that Zs by measurement is a design concept. On a working installation I want the zs to include the parallel paths, the protection device impedances and anything else that is thrown in, as that is what the installation will be at when a fault occurs, not some calculation on a piece of paper, their answer "Should avoid live testing or work when it is not necessary"
 
heartily agree with both of you malcolm & widdler. A fault occurring sees the RCD, MCB, and all parallel paths, so Zs should be measured. what could be worrying is when trhe calcoulated value is within the max. allowed, but the measured value is not. will the protective device trip within the specified time. ?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
meggar 1552 zs test
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
23

Thread Tags

Advert

Thread statistics

Created
kevinjstanley,
Last reply from
telectrix,
Replies
23
Views
4,853

Advert