Hi I've just moved testers from fluke to megger 1553, just wondering if the socket test lead measures the R1 & Rn reading when testing a ring main. The R1 + R2 reads ok just wondering if I need to purchase a Kewtech R2 mains adapter Thanks
 
Hi Simon,

The mains test lead from the MFT1553 cannot beused for measuring R1+Rn but you can use the SIA10 mains test lead or a mainsadaptor as you mentioned.
 
Not sure if this is of any help but I have just go hold of a Megger 1730 and was wondering the same thing. I was informed by Megger to use the lead with the plug attachment and as this comes with 3 separate leads on the end. So you only plug the leads you need into the meter.
 
Not sure if this is of any help but I have just go hold of a Megger 1730 and was wondering the same thing. I was informed by Megger to use the lead with the plug attachment and as this comes with 3 separate leads on the end. So you only plug the leads you need into the meter.

Thats right th 1700 series has that lead where as the 1500 series didn't. I bought the lead with the 3 separate plugs on as an extra afterwards.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Megger socket test lead
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Thread Tags

Advert

Thread statistics

Created
Simon Hall,
Last reply from
Amp David,
Replies
5
Views
1,521

Advert