I’ve recently seen a motor wired directly from the local isolator to the motor terminal box in 3 core 1.5mm cable. The gland has been made off into a threaded hole in the motor terminal box and at the isolator end directly connected to the incoming swa from the MCC by means using a flylead. My question is is this a sufficient for earthing the motor. My understanding is you can use the armour as a cpc but wasn’t sure if any additional “fly leads” should be fitted at the motor end?
 
it may well be ok, have you tested the earth continuity?

there is little point in adding a fly lead if the gland is directly screwed into the device.
 
it may well be ok, have you tested the earth continuity?

there is little point in adding a fly lead if the gland is directly screwed into the device.
Yeah earth continuity from the motor terminal earth to the isolator is coming up as 0.01 ohms
 
Yeah earth continuity from the motor terminal earth to the isolator is coming up as 0.01 ohms. I’ve just seen sometimes flyleads coming of the gland to the main chassis of the motor what would the reason for this be?

Thank you
 
years ago, and it is still possible now but rarely done,

entire installations were done in rigid steel conduit.
the conduit would be the earth, all the cables inside would be phase or neutral.

extra earth cables were rarely added as the earth resistance through the conduits was normally better than you could achieve with an earth cable of equal or smaller csa to the live conductors.

the only time fly leads were added was if the fitting or device being powered needed an earth and it was not directly bolted to the conduit.
 
  • Like
Reactions: Jako13!
because they have always done it like this,

think back to basics, if you have a bolted connection to the motor terminal box, that is then bolted to the motor itself, you are likely to have a better connection and lower resistance than any fly lead could achieve.

also, if the terminal box is plastic then a fly lead would be required.
 
  • Like
Reactions: Jako13!
because they have always done it like this,

think back to basics, if you have a bolted connection to the motor terminal box, that is then bolted to the motor itself, you are likely to have a better connection and lower resistance than any fly lead could achieve.

also, if the terminal box is plastic then a fly lead would be required.
Thank you James
 
  • Like
Reactions: James

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Maintenance Electrician

Thread Information

Title
Motor earth
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Jako13!,
Last reply from
Jako13!,
Replies
6
Views
1,509

Advert