Hi Midwest, I've just asked our repairs manager about this; we can fix most MFT issues in our calibration lab so it's very, very rare we would send them to Megger. (It would be something like needing new costly PCBs for us to do that.) All our repairs do also come back calibrated.

We're always happy to investigate and provide a no obligation quote or advise of other options moving forward.
Thanks for the reply. My issues, not yours, was turn around time and getting my meter back. So it had to go straight to Megger. Couldn’t take the chance you couldn’t fix.
 
  • Like
Reactions: Admin
Thanks for the reply. My issues, not yours, was turn around time and getting my meter back. So it had to go straight to Megger. Couldn’t take the chance you couldn’t fix.

No problem, I understand that.

In case you ever have need for repairs in the future, our turnaround time is normally very good, plus we usually use DPD to get things dispatched quickly. It's rare we can't fix things inhouse so if you ever need to send anything in, we'll always try give you a cost/time estimate as soon as we diagnose the issue. (Oh and we have hire equipment here too so if there was going to be a delay, I'm sure we could sort you out!)
 
  • Like
  • Winner
Reactions: Admin and telectrix
An Affordable 2nd hand Fluke 1651B , for idiot proof low ohms testing.
( not as thorough as hi current surge PAT testers did, for earth continuity- but more useful !)
 
I'm currently running a Di-Log DL9083p And a trusty old megger mft1552 both very usable testers imho. I do love the megger more for consistency, especially as it has the high current loop test and 1000v insulation test. But for domestic stuff the di-log is perfect except it's missing a neck strap!
 
  • Like
Reactions: static zap
Megger 1720 since 2014 - hasn't skipped a beat!
 
Fluke 1653
Been great and in use for 9 years so far
 
Trusty old Dilog 9083P. Bought used from another spark who was upgrading. Very easy to use which makes it ideal for me. Worked well for 3 years and sails through its annual calibration.
I also have one of these, getting on for five years old and still fine, recently calibrated OK.

It's a bit clunky and not at all sexy but it does all the tests only thing it's missing is a 1MOhm IR function.

I would genuinely like to know what makes the other £400-£600 pounds, to get the Meggers and Flukes, worthwhile.
 
I would genuinely like to know what makes the other £400-£600 pounds, to get the Meggers and Flukes, worthwhile.
Sometimes if doesn't have to - it depends on an individual or businesses circumstances, for example:
Dilog 9083P £325+vat
Megger 1741 £875+vat
The Megger is £550 more than the Dilog.
For a business, an MFT is a capital expenditure as opposed to a revenue item.
Typically a business will apply the '25% reducing balance' method of depreciation.
In year one (the year of purchase), the Dilog would charge £81.25 depreciation to the P&L and retain £243.75 on the balance sheet as fixed assets. Whereas the Megger would charge £218.75 depreciation and carry forward £656.25 asset value. So in year one, the Megger has actually only cost you £137.50 more, i.e. less than one typical morning's work, to have the latest tool you fancy, drool over and work hard for.
Fast forward to 2024 when Megger bring out their newer flagship MFT, the book value on the balance sheet of your 1741 is just £155, but the street price for a second hand one is still around £400 and every apprentice wants one, so you easily make £250 profit on resale when you sell it, which offsets against the year one depreciation on your new tester.
Conversely the residual value on secondary and tertiary brands, is often beneath the 25% reducing balance curve, giving you little or no profit on disposal.
 
Sometimes if doesn't have to - it depends on an individual or businesses circumstances, for example:
Dilog 9083P £325+vat
Megger 1741 £875+vat
The Megger is £550 more than the Dilog.
For a business, an MFT is a capital expenditure as opposed to a revenue item.
Typically a business will apply the '25% reducing balance' method of depreciation.
In year one (the year of purchase), the Dilog would charge £81.25 depreciation to the P&L and retain £243.75 on the balance sheet as fixed assets. Whereas the Megger would charge £218.75 depreciation and carry forward £656.25 asset value. So in year one, the Megger has actually only cost you £137.50 more, i.e. less than one typical morning's work, to have the latest tool you fancy, drool over and work hard for.
Fast forward to 2024 when Megger bring out their newer flagship MFT, the book value on the balance sheet of your 1741 is just £155, but the street price for a second hand one is still around £400 and every apprentice wants one, so you easily make £250 profit on resale when you sell it, which offsets against the year one depreciation on your new tester.
Conversely the residual value on secondary and tertiary brands, is often beneath the 25% reducing balance curve, giving you little or no profit on disposal.
Okay, so i make a £10,000 MFT with few discernable benefits over a £325 one yet they'll sell like hot cakes?
 
Okay, so i make a £10,000 MFT with few discernable benefits over a £325 one yet they'll sell like hot cakes?
Probably stretching a point there.
But (crystal ball time) when AFDDs are perfected and made mandatory for new circuits >=32A in the 19th Edition in 2025 and Megger launch their shiny new £1,600 MFT1951 with onboard arc fault simulation, they will sell loads of them.
 
Ethos 8400.
The leads are pants, tried to buy megger leads for quality, but on the Ethos the blue/green leads have to be piggy backed for a high current Zs test, which the megger leads don't do. A big downside is that the no trip test is strictly 3 wire, which means you cant test at switches on RCD protected circuits, that's a real disadvantage. The IR test is not press and hold, it does a test over a few seconds and averages. That's a disadvantage for fault finding because I want to hold 500v on the fault for a while, if it starts low and rises that's usually damp....I cant use my experience of what the meter is telling me. Eats batteries as well.
Mines been back to Ethos twice (had it less than a year). The last time because Zs readings always came back as 0.01 ohms....(PFC off the scale!). They sent back a new meter with the old serial number peeled off and applied to the new meter. On the plus side the auto RCD test is awesome.
Based on my experience I'd say don't buy.
 
I've had a metrel eurotest for about 15 years now without a glitch.
Also got a megger 1720 and kewtech, we had a megger 1730 until one of the lads dropped it, megger wanted £ 250.00 just to look at it , from what I've heard it's their standard reply. It's still sat in the office waiting for me to make a decision.
I had a similar problem with a 3 month old 1711, they are a beautiful instrument to use, but do appear to be susceptible to drops. I pointed out there advertising shows a truck driving over a 1700 series and survives. They were adamant that as the drop was 1.2 metres, it wasn't covered by warranty.
I then purchased a 1721, and within a day or two, Megger had a change of heart and offered to repair my 1711 free of charge - of which they did.
Anyone want to buy a perfectly good 1711?
Be persistent with Megger, I'm sure they wouldn't want the bad publicity.
 
  • Like
Reactions: GMES
Thanks for the plug Dan - if anyone does want any info, we're always happy to help people find the right tester and we do have a fair few MFTs in stock to choose from!;)




We're always happy to provide a competitive, no obligation quote for repairs.
Just drop us a message on [email protected] or call 0113 248 9966 - ideally with a fault description - and we'll see what we can do!

Would you have any advice for a mature trainee as to which multifunction tester to go for, that would be value for money, but a worthwhile investment?
 
my 1553 is 11 years old. never failed, never been repaired, and has passed every calibration.
 
my 1553 is 11 years old. never failed, never been repaired, and has passed every calibration.
Hope you had your fingers crossed when yo said that!
 
  • Like
Reactions: static zap
my 1553 is 11 years old. never failed,
... Respected for its worth - and probably never dropped 2m onto a painted concrete floor ...
Life expectancy must depend on part if it treated kindly , or slung in back of van jostling with reels of T&E.
 
my 1553 is 11 years old. never failed, never been repaired, and has passed every calibration.
My 1552 is 9 years old, had the cable plugs repaired once but apart from that has never missed a beat.

Except last month when testing a TPN board full of RCBOs, it got a bit warm after the twentieth time test... ?
 
  • Like
Reactions: static zap
I have a 3 piece Robin set , had it over 15 years now
Yeah me too dusty . Does the job just as well as my fluke 1642 and no probs with calibration
 
... Respected for its worth - and probably never dropped 2m onto a painted concrete floor ...
Life expectancy must depend on part if it treated kindly , or slung in back of van jostling with reels of T&E.
mine is kept in a padded camera case. for fault finding i use a IR/cont. Megger BM summat, cost a tenner faulty. all it was was a broken connection on the inside of the lead socket. passed calibration and if i drop it it's only 4 pints lost.
 
Megger 1741, 1735, 1731 and a Metrel 3155 eurotest
Do you still have them all Richy?
Don't worry I'm not looking for a freebie like last time, just interested ?
I have a 1731 which I love. The metrel mi3000 lasted quite a few years though and was adequate, it's now kept as a spare.
 
  • Like
Reactions: ruston
HI
Just looking at buying a metrel ML3155 XD
would anyone happen to know what the difference between the standard kit and the euro kit is. for the £400 difference

thanks
 
I have an embarrassingly large collection of devices,some for work,some for fun,but in the latter MFT club,i have a 1720,with the latest version download,which has been very good.

I took the time to learn it's every option,and would keep it,even on a future upgrade,which will probably arrive out of giddyness,more than need ;)

I would always stress the need to know whatever device,100%,rather than chase any dazzling,newer versions.

In the last month,i have used a DC current meter,and an inclined manometer,both of which,are older than me mum :cool:
 
@happyhippydad Morning. Happy new year. Yes we still have all those test instruments. The Megger is the daily go to and to date the Metrel has been used mainly on EV testing with additional extra bits; but I am going to take it on as my main tester sometime soon.

We have a lot of Megger test equipment (clamps, earth leakage, AVO, iClamps, PAT testers etc) but these last couple of years have felt the MFT's are not made as well as they used to be.

The last 1700 series we ordered arrived with the top and bottom detached! It was all sorted out OK but knocks your confidence in the equipment somewhat.
[automerge]1577962855[/automerge]
HI
Just looking at buying a metrel ML3155 XD
would anyone happen to know what the difference between the standard kit and the euro kit is. for the £400 difference

thanks
@rlsecurity if you look on the meter UK website there is a chart showing what is and isn't included. Scroll down to the bottom of this page:

 
Kewtech KT65 for last 3 years. It’s been reliable and we understand each other. I do have Megger envy building, but the KT just won’t die :) .
That KT65 was one of the few I considered before pitching for a lightly used Megger 1730. Looks nice and fool-proof compared to the Mettrel and Fluke Had a Fluke on loan recently. Can't say much about the accuracy, which should the the most important consideration, but find the 1730's "child's toy" controls far easier to set correctly.

Does anyone else test their MFT against a Cal-Card and a known RCD? Mine gets a run through and spreadsheet log roughly every month. Give me a heads up as to potential issues.
 
Does anyone else test their MFT against a Cal-Card and a known RCD? Mine gets a run through and spreadsheet log roughly every month. Give me a heads up as to potential issues.

That’s what I did when registered with a Scheme. Then every third year, I’d have it calibrated. I replaced the Calcard then, but then someone pointed out the card is just a set of known resistances, which can’t alter.
As did a Zs test as well as RCD test on the same socket. If was doing it now, I would install a dedicated socket on its own RCBO, to save messing around isolating devices.
 
  • Like
Reactions: Marti
That’s what I did when registered with a Scheme. Then every third year, I’d have it calibrated..
THAT'S INTERESTING! I hadn't realised that if you monitor the readings and they remain the same it isn't necessary to fork out anything between £50 - £125 every year for a calibration test. Thanks Midwest.
 
If you are with a Scheme, just clarify what they require. I was with Elecsa, and purchased my CalCard from them.
 
Personally I advocate annual calibration in addition to ongoing accuracy checks. These are nowhere near as thorough or controlled as the calibration process.

It's all academic for me anyway as RECI require annual calibration without exception.
 
  • Like
Reactions: 123
On my last three NICEIC visits they have changed their minds each time
Was every 3 years
Then endless if I had my own proving unit,
now back to every year.
 
  • Informative
Reactions: Midwest
KT65, selector switch went in warranty, that was just dirt , it does get used in some nasty industrial locations, since then its now over 9 years old still going strong, have another KT65 as back up but never been out of the house.
Only other thing is one of the leads broke
 
  • Informative
Reactions: Marti
Matrel 61557, does all & more, passes calibration every year.
 
The new kewtech kt63 + I think it is looks pretty damn good... Has built in dc testing for rcds which is good as we are moving towards type a etc.... Most can't test them... Only the ac side... Its nearly £1k though
 
I have a Megger MFT 1741-BS. Had a Megger MFT 1553 before that. (Still have it as a backup.) New one is much faster and also has rechargeable batteries. Great instrument, although some would still swear by the 1500 series over the 1700 series.
Speak to Megger and get it upgraded to the new 1741+ I think they will do it for a low price....
 
Speak to Megger and get it upgraded to the new 1741+ I think they will do it for a low price....
Do they offer a deal on upgrading to the 1741+?

I'll be honest - I was fuming when I found out that it had been released as I've only had my 1741 just over a year and would have bought the 1741+ had it existed at the time. (I see there's a nice limited edition black version of it too...)
 
A couple of Megger 1553s one with Bluetooth feature that was used once.
interested to hear that Megger potentially do an subsidised upgrade to the 1700 series. Does anyone have any idea how to go about it.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Admin

Staff member
Admin
Mod
Joined
Location
Staffordshire
Website
https://www.electriciansforums.net
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Not an electrician at all.
Business Name
Ekthetikos

Thread Information

Title
Multifunctional Testers - Which one have you got and how long has it lasted?
Prefix
N/A
Forum
Electrical Tools and Products
Start date
Last reply date
Replies
210

Advert

Thread statistics

Created
Admin,
Last reply from
Lister1987,
Replies
210
Views
101,041

Advert