I am currently testing a 2 bed flat, all other circuits read clear. Flat Ring not so much.

Using a Megger MFT1721

L - E Reading 300Mohms but slowly
L - N Reading 400 Mohms but slowly
N -E Reading 200Mohms but slowly

Have tried breaking the ring and narrowing down the problem but both sides come up with higher readings.

Have replaced half the ring and still no change.
Each leg reads +999
You pit a couple of sockets together it starts to drop. Tried replacing parts of ring with 2.5 to see if I can clear it but its not working.

Trying replacing a lag at a time tomorrow...

The plot is a new build so I would expect the readings to jump above 300 right away, so slow readings mean I'm having to investigate.

Does anyone here have any idea what could be causing these readings?
 
If it is slowly creeping upwards it’s probably just dampness from the plaster drying out, loosen all the sockets a little bit and leave it for a few days if you are worried.
 
I am currently testing a 2 bed flat, all other circuits read clear. Flat Ring not so much.

Using a Megger MFT1721

L - E Reading 300Mohms but slowly
L - N Reading 400 Mohms but slowly
N -E Reading 200Mohms but slowly

Have tried breaking the ring and narrowing down the problem but both sides come up with higher readings.

Have replaced half the ring and still no change.
Each leg reads +999
You pit a couple of sockets together it starts to drop. Tried replacing parts of ring with 2.5 to see if I can clear it but its not working.

Trying replacing a lag at a time tomorrow...

The plot is a new build so I would expect the readings to jump above 300 right away, so slow readings mean I'm having to investigate.

Does anyone here have any idea what could be causing these readings?
Damp
 
I am currently testing a 2 bed flat, all other circuits read clear. Flat Ring not so much.

Using a Megger MFT1721

L - E Reading 300Mohms but slowly
L - N Reading 400 Mohms but slowly
N -E Reading 200Mohms but slowly

Have tried breaking the ring and narrowing down the problem but both sides come up with higher readings.

Have replaced half the ring and still no change.
Each leg reads +999
You pit a couple of sockets together it starts to drop. Tried replacing parts of ring with 2.5 to see if I can clear it but its not working.

Trying replacing a lag at a time tomorrow...

The plot is a new build so I would expect the readings to jump above 300 right away, so slow readings mean I'm having to investigate.

Does anyone here have any idea what could be causing these readings?
Not sure I understand "replaced part of Ring with 2.5??"
 
I am currently testing a 2 bed flat, all other circuits read clear. Flat Ring not so much.

Using a Megger MFT1721

L - E Reading 300Mohms but slowly
L - N Reading 400 Mohms but slowly
N -E Reading 200Mohms but slowly

Have tried breaking the ring and narrowing down the problem but both sides come up with higher readings.

Have replaced half the ring and still no change.
Each leg reads +999
You pit a couple of sockets together it starts to drop. Tried replacing parts of ring with 2.5 to see if I can clear it but its not working.

Trying replacing a lag at a time tomorrow...

The plot is a new build so I would expect the readings to jump above 300 right away, so slow readings mean I'm having to investigate.

Does anyone here have any idea what could be causing these readings?
So let me get this straight in my head, you have taken all the accessories off the RFC? IR tested each leg of the RFC? all >999Mohm, put the accessories back on, screwed them back and the IR readings slowly rise to around 300Mohm? if thats the case then a pound to a pinch of the brown stuff it's damp walls, a new build you said?
 
  • Like
Reactions: ruston
So let me get this straight in my head, you have taken all the accessories off the RFC? IR tested each leg of the RFC? all >999Mohm, put the accessories back on, screwed them back and the IR readings slowly rise to around 300Mohm? if thats the case then a pound to a pinch of the brown stuff it's damp walls, a new build you said?

Yep. New build.
 
You are looking for and trying to rectify a problem which does not exist.
 
I don't think I'd be worried about the odd 100,000,000 ohms, either.
 
Why are we discussing 200,000,000+ Ohms readings?
 
  • Agree
Reactions: 123
I use an analogue meter, as long as I don't see the needle with my right eye all is fine.
 
I use an analogue meter, as long as I don't see the needle with my right eye all is fine.
......Always thought you were a bit of a winker.;)
 
  • Funny
  • Like
Reactions: DPG and westward10
Anything above 2 meg ohms is acceptable .....
Not too sure I'd be happy with that on a rewire or new install, damp from plaster or not.
 
  • Like
Reactions: DPG
Not too sure I'd be happy with that on a rewire or new install, damp from plaster or not.
Surely this comes from the experience of un-doing all the sockets , letting them breath , getting a much better reading .. logic .
( if worried about tracking damage - I can see AFDs turning up sooner)
Is this "Damp from New Build plaster" effect common only in hot weather ?
 
if it's a new build, it won't only be the plaster drying. the roof will leak. the plumbing willl leak, the plasterboard will be mouldy.
 
any rate, my megger BM80 goes up to 100Gig on the 500V range, so ner,ner. :D:D:D.
 
  • Funny
Reactions: Baker1988

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email