Working on a tt installation with resistance reading in excess of 200 ohms.
MCBs are single pole, neutrals on common bar. Newly installed 'cheap' rcd is double pole.
Rcd is tripping, but not consistantly. Have isolated possible circuit fault is on, but cannot find any obvious reason for tripping.
Possible N-E fault from another circuit?
 
Working on a tt installation with resistance reading in excess of 200 ohms.
MCBs are single pole, neutrals on common bar. Newly installed 'cheap' rcd is double pole.
Rcd is tripping, but not consistantly. Have isolated possible circuit fault is on, but cannot find any obvious reason for tripping.
Possible N-E fault from another circuit?

Who knows, not enough to go on. What tests have you done? Who installed the "cheap" RCD? the questions are almost endless
 
  • Like
Reactions: 1 person
When you say a TT with a resistance >200ohms, how much greater and are you testing the Ra value or are you including parallel paths? When you tried to localise the fault did you use a mega tester? What IR readings did you get?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
rcd tripping
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
PaulW,
Last reply from
Marvo,
Replies
2
Views
1,247

Advert