adonis2

~
DIY
Jul 23, 2017
31
47
93
41
Essex
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
Another hob wiring question sorry,

I am replacing my oven and hob and the oven connections was fine, 6mm from new consumer unit on a 32a RCBO split to oven and hob.
the new hob is 6.2kw, old hob is 6kw the new one will not take the 6mm cable that was connected to the previous hob and the instructions say use 2.5mm cable.

I would like to use 4mm cable minimum due to the 32a RCBO what cable do you recommend if this is ok?
The links between the connectors are still in place.

I have attached pics.

Thanks
20220509_133741.jpg

20220512_122122.jpg
20220509_115841.jpg
 
2.5mm seems small, though with diversity it would be 10 + 0.4 * (27.4 - 10) = 17A so usually OK.

I certainly would look at 4mm, or at least a 2.5mm that is rated for 90C operation such as the LSZH version of T&E. For example, here it is sold by the metre (both 2.5mm and 4mm below):
Also high temperature flexible cable:
 
Check H07RN-F 85deg. 2.5mm is rated at 27A. Given the short length of your cable and diversity already mentioned it will be fine
 
  • Like
Reactions: pc1966
as said 2.5 flex of a heat resisting type is adequate but if you're not pleased about it, if you look hard you'll find 5x2.5 so you can double up for 2x L, 2x N, leave the links in. I carry a bit specifically for hobs as the stupid terminal setups are often made for continental polyphase installs.
 
  • Like
Reactions: brianmoooore

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

adonis2

DIY
~
Joined
Location
Essex
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Replacement Hob Wire size
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
adonis2,
Last reply from
Teddy Lop,
Replies
4
Views
3,852

Advert