OP
Peggyhenry89
DIY
- Reaction score
- 5
Sorry I don't know exactly when it was first installed but I could have been 80s perhaps and I unfortunately do not have any pics of the original install.Yes, test results say there is in one column but no test times, etc, for that, and the lack of RCD aspect is there as a C3 point.
Do you have a photo showing an RCD was actually present?
My suspicion is there was none but the form was auto-filled to have that column completed. Do you know when that installation was dated from?
Ze would be the "means of earthing" alone so could be 24 ohms as quite reasonable for a rod or two.
Zs is the in-use impedance with any bonding, etc, present. Are there measure Zs figures for individual circuits? They would show if bonding was taking the figure down to < 1 ohm, etc.
It is not uncommon for pipe work to be bonded in other nearby properties to a TN-C-S or TN-S system and so they can well drop the impedance down that way, but it is not reliable as anyone anywhere on the system can make a repair and not maintain electrical continuity quite legitimately.
Either way. The lack of RCDs is not down as a C2 and even if it was the statement saying that the complete rewire of both flat and shop is misleading.
Thanks for your advice. I'm still pretty new to this but if my parents have been scammed I'd like to pursue it. Although I will admit that we were all a but naive at the time and should've questioned it but we put our trust in the letting agent and the inspector