Hey guys, hoping someone can help with my problem.! A client of mine asked me to rig-up a little solar system to power a diaphragm air pump (230V/3A) for a cesspit.
Solar/low voltage isn't something that I'm that familiar with (I'm a sparks), would have much rather just laid some new armoured down to the pump!

I set up a 12V/300W solar panel, which feeds a voltage regulator which in turn is connected to 2 x 60aH 12V batteries. The batteries are wired in parallel, which then feed a 3000W pure sine wave inverter (12V - 230V). Was hoping this would be enough to run the air pump for most of the daylight hours, but seems to cut out after about 1.5 hours.

Will more batteries solve the problem do you think? I reckoned that the 2 batteries should have been enough, with the solar panel topping up the charge throughout the day.

Ant advice would be greatly appreciated.
 
230V at 3A is 690W before you look at losses, so your 300W panel will never be enough.
Also at night you need something to switch it off otherwise the batteries will be discharged and will be damaged.
 
Upvote 0
230V at 3A is 690W before you look at losses, so your 300W panel will never be enough.
Also at night you need something to switch it off otherwise the batteries will be discharged and will be damaged.
Do have a timer in place.
 
Upvote 0

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Thread statistics

Created
sponge23,
Last reply from
sponge23,
Replies
2
Views
1,610

Advert