Had a ring circuit with a spur feeding a 2 gang socket coming directly from the 32a mcb. Ring main has since been stripped out and just left with the spur. I have now fitted a 2 gang socket in 4mm directly below the cu, is it still acceptable to leave the 2.5 spur coming off the same 32a mcb?
 
Yes as long as it is only for a single or double socket outlet or FCU.
 