Hi all. I'm new here and after some help please...

I'm currently wiring an old house as complete renovation progresses. The house is to be divided into two some time in the distant future, so two separate consumer units are being fitted. But, for now, there is to be just one (existing) 100amp supply to the property. I have wired the first 'half' of the house and need advise on the best way to run a submain to the next CU. The client does not wish to use SWA prefering not to have cables visible. Therefore, I'm considering running 10mm twin/earth through the floor structure of the building. I realise that this will need to be RCD'd but need advice on the best way to do this. Could the submain be run from a 40amp 30ma RCBO in the first consumer unit or does it need double pole isolation as well? I realise that there will be no discrimination from the CU at the other end of the submain but not sure there's anything I can do about this!

This is a TT system, and the demand is very low. No showers or electric heating. All energy efficient lighting. I am sure that the 100amp supply is sufficient for the two installations.

Any advise much appreciated :-)
 
Spin doesn't BS 8436 still have issues with the size of protection device it can utilise and it's fault current limit of less than 200amps? Or have these issues been recitified
 
I believe that many of the issues have been adressed yes.
Although I believe the advice is still that the cable is only suitable for use with Type B MCBs/RCBOs.
 
30mA RCD protection is only required for cables concealled in walls at a depth less than 50mm, which don't have any other form of additional protection.
You haven't yet indicated that the cables will be concealled in any walls.
SWA isn't the only cable that has an earthed outer sheath, you could also use a BS8436 cable such as Flexishield or Guardian.

I have said that the cables will be concealed in the floor, under floorboards...which has the same implications as being concealed in the wall.
Flexishield is great, but only upto 6mm (32 amp) which is not big enough. 40A is required here. :)
 
Last edited by a moderator:
I have said that the cables will be concealed in the floor, under floorboards...which has the same implications as being concealed in the wall.
Flexishield is great, but only upto 6mm (32 amp) which is not big enough. 40A is required here. :)
No it doesn't have the same implications as being concealled in a wall.
It is only cables concealled in a wall, and in safe zones that are required to have 30mA RCD protection.
6mm² BS8426 has a current rating of 58A when clipped direct, and you can now obtain 10mm² cable.
 
Electrical & Physical Data | Flexishield not according to their data a 6mm can take up to 63amp on a tray and I would reckon you wouldn't be far off for erection methods F and G.

If I can persuade them not to stuff the floor around the cable with insulation then maybe this will be possible! I've never used this stuff, how is it terminated with regards to the aluminium tape? Surely this has to be earthed in order for it to be suitable for use without the need for RCD protection?
 
It is terminated in a similar manner to T&E or FP200.
There is a bare earth conductor through the cable which is in contact with the shield.
With regards to the RCD protection, I suggest you refer to either Regulation 522.6.8 or 522.6.100 (amendment 1), and you will not that RCD protection is not an acceptable means of protecting the cable.
As such, the use of one without any of the other allowable means of additional protection would be a departure, and you as the designer would have to attest that the same degree of safety will be provided as would be achieved by compliance with the Regulations.
 
No it doesn't have the same implications as being concealled in a wall.
It is only cables concealled in a wall, and in safe zones that are required to have 30mA RCD protection.
6mm² BS8426 has a current rating of 58A when clipped direct, and you can now obtain 10mm² cable.

This surprises me. I have always assumed that being concealed in a wall, or under a wooden floor, would carry the same degree of risk. I have just confirmed with niceic guy who agrees that it seems a little silly, but you're absolutely right. :)
 
So, I don't need any special gland to earth the aluminium tube, and I can terminate straight into an MCB in the CU. Niceic guy also said that it doesn't need double pole protection if straight from the CU. For piece of mind I will replace the main switch in the CU with a time delayed RCD.
All I need to do now is find somewhere who will sell me a 25 meter length of Flexishield!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Colin33

Arms
~
Joined
Location
Cornwall
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Submain ?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
30
Unsolved
--

Thread Tags

Tags Tags
submain

Advert

Thread statistics

Created
xt600,
Last reply from
xt600,
Replies
30
Views
4,134

Advert