I've read that article before, it does make some sense, though I'm not sure, personally that fitting the upstream S has downsides to be avoiding.
Often on a TT it is the provided a means of isolation before the board which is always handy.
It's also handy that it helps you meet the disconnection times for a submain on the install, so you can fit say a garage supply from an MCB in the main board (assuming it's not buried <50mm in a wall, or any other means of installation requiring 30ma RCD protection).
You can then have a couple of upstream RCBO circuits in the garage and still maintain selectivity.
An upfront rcd whether it be delayed or not will only give partial selectivity.I'm a fan, personally of local RCBOs in the garage as I want to lights to stay on ideally if the sockets were to go while I have a welder or grinder or similar in my hands. (Of course the downside being any fault on the submain cable itself will take out the entire house, given the MCB is as likely as good as useless).