I have an armour cable out to a garden hut and used a RCD 2 way consumer unit.

The supply comes from an MCB in the consumer unit into a rcd/spur and out on the armour cable.

There are 2 rcds I know. Would you use a fused spur on its own to protect the armour cable (instead of the rcd/spur) and would a standard fuse provide discrimination to avoid nuisance tripping?

As always comments appreciated.
 
i wouldnt neccesarly use an FCU. i would joint it an thats it. no need to introduce more protective devices into the circuit that are not needed. Also the MCB would react long before the fuse thought about it IMO. This is assuming of course that the supply cable to the SWA doesnt require RCD protection, and that you will provide RCD protection to the final circuits at the other end, if its needed.
 
Depending on where the CU is situated, the swa could be glanded to the CU itself and then fed straight to the hut, dependant on CU brand, type, location, etc..
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Supply to a garden hut
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
14
Unsolved
--

Advert

Thread statistics

Created
Bul,
Last reply from
johnboy6083,
Replies
14
Views
2,206

Advert