Can an swa be buried outside prescribed zone? Not rcd protected!
 
When I saw the thread title I thought the OP had dropped his hacksaw in a trench and was wondering how to retrieve it !


PS, how do I add smilies ?
 
I have! Haha.. Bloody spellcheck! Any input gentlemen any1 daring to give their view.?
 
Swa is OK for outside zone with no RCD as long as other Regs don't require the protection for other reasons ...i.e. special locations etc
 
Not within special location, drilled through outside wall then chased in approx 500mm down wall to floorboards at a depth greater than 50mm. I wouldnt see a problem exept it was 50mm 4core 160A feeding hotel control panel..
 
Swa is OK for outside zone with no RCD as long as other Regs don't require the protection for other reasons ...i.e. special locations etc
Ooh, good answer. :)

I would add, "...assuming that the armour is earthed..."
 
Last edited:
  • Like
Reactions: 1 person
Not within special location, drilled through outside wall then chased in approx 500mm down wall to floorboards at a depth greater than 50mm. I wouldnt see a problem exept it was 50mm 4core 160A feeding hotel control panel..

As long as it length and ccc complied to installation methods then ok, if it was run in an area prone to possible drilling for whatever reason then it would be wise to have a layout plan of the cable run available for any contractors likely to work in the area.
 
I thin on that note it goes without saying :)
You'd kinda hope, wouldn't you? :) But then... *

* absolutely in no way a comment on the original post/poster, just a general musing... ;)
 
  • Like
Reactions: 1 person
Not within special location, drilled through outside wall then chased in approx 500mm down wall to floorboards at a depth greater than 50mm. I wouldnt see a problem exept it was 50mm 4core 160A feeding hotel control panel..

Just to confirm, the buried cable is greater than 50mm from the surface of the wall? Daz
 
The use of SWA is one of the acceptable methods for concealing cables in walls.
Obviously the armour has to be earthed.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

bigspark17

Arms
~
Joined
Location
wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Swa buried
Prefix
N/A
Forum
Electrician Forum
Start date
Last reply date
Replies
12

Thread Tags

Tags Tags
buried swa

Advert

Thread statistics

Created
bigspark17,
Last reply from
Deleted member 26818,
Replies
12
Views
1,713

Advert