a bit of 2H10

*No protection required
*Chase with a finger chisel
*Includes 24mm² CPC
*45mm bending radius
*Stays where you put it unlike those huge black plastic snakes that leap up and bite you

Or 2H16 up to 100A
 
  • Like
Reactions: 4 people
IMG_0788.jpgIMG_0789.jpg


As Dillb said drill down at an angle to get you under the floor . On this job i stitch drilled out a 3rd of a brick on a downward angle . If the existing gas meter had been in a recessed box i would have followed suit .
 
*No protection required
*Chase with a finger chisel
*Includes 24mm² CPC
*45mm bending radius
*Stays where you put it unlike those huge black plastic snakes that leap up and bite you

Or 2H16 up to 100A

2H16 is the biggest ive done, 19L1.5 in multi.
 
View attachment 30528View attachment 30529


As Dillb said drill down at an angle to get you under the floor . On this job i stitch drilled out a 3rd of a brick on a downward angle . If the existing gas meter had been in a recessed box i would have followed suit .

Waw have you really installed another meter box next to dno box! If you have that is shocking imo. Put ur switch fuse in the dno box, if its on. The owners property its theirs not dno so you may add your sw fuse in there! Flobbogasted at that pic!!
 
Waw have you really installed another meter box next to dno box! If you have that is shocking imo. Put ur switch fuse in the dno box, if its on. The owners property its theirs not dno so you may add your sw fuse in there! Flobbogasted at that pic!!


Looks like a gas box not electric.

There is a G written on it.
 
  • Like
Reactions: 1 person
So its comon practice to mount isolator armoured and ipbox in a gas meter chamber??
 
Dont see how its relevant as op has stated db is gunna be 8M away so irrelevant! If you use a cable capable of taking the dno full service fuse isolate it at that rating

It would be poor design to have no discrimination between the DNO fuse and the one you put in. It would be best to leave s gap of one fuse size so take it to 63A. Are you suggesting that it's ok to have two 100A fuses in line? Yes it might well protect the cable but it's not a great idea.

its not irrelevant.
 
It would be poor design to have no discrimination between the DNO fuse and the one you put in. It would be best to leave s gap of one fuse size so take it to 63A. Are you suggesting that it's ok to have two 100A fuses in line? Yes it might well protect the cable but it's not a great idea.

its not irrelevant.


Excuse me? So your suggesting using dno full capacity in one post then slating use of it in another.? Why is it bad practice fusing your submain at same as dno cutout on a capable ccc cable,? Can u explain?
 
Excuse me? So your suggesting using dno full capacity in one post then slating use of it in another.? Why is it bad practice fusing your submain at same as dno cutout on a capable ccc cable,? Can u explain?


You never heard of discrimination?
 
You never heard of discrimination?

How would you go about achieving full discrimination between the DNO fuse and the one in the switch fuse then on a domestic setup such as the OP's? IMO it will be nigh on impossible.
 
Last edited by a moderator:
The total let through energy of the downstream fuse will have to be less than the pre-arcing energy of the upstream fuse to achieve full discrimination.
 
Last edited by a moderator:
  • Like
Reactions: 1 person
Interesting discussion on discrimination, a question I've asked myself before, and received conflicting replies.

The meter box belongs to the owner of the property, but the DNO has certain requirements; BS 8567 (gas is BS 8499).

I asked my DNO (SSE) before on what they would expect to see in such a situation, as here. I asked DNO what would they say about extended tails, 'We would expect a switch fuse, as it is a submain'. Could I put equipment in said box, answer 'No not really, what are you thinking of? Switch fuse? 'Ahhh, okay'.

Considering size of fuse in switch fuse (i.e. DNO 100a, switch fuse 80a), I asked Elecsa tech support for advice;

'Without referring to the time current characteristics of each device for the exact information we believe that the fault protection characteristics of each device will be similar but not the same.

They do provide fault and overload protection for the whole installation. Therefore there will certainly some discrimination with overload protection.

The final decision regarding the discrimination of the two devices would be down to the designer of the installation'.
 
might be an idea to use a MCCB instead of a sw.fuse. cost permitting. this should ensure the MCCB tripping before the \DNO fuse. discuss?
 
might be an idea to use a MCCB instead of a sw.fuse. cost permitting. this should ensure the MCCB tripping before the \DNO fuse. discuss?

Mccb would clearly take out the supply before dno fuse. Domestically 80A is usially suffiecent but with some customers adding multiple electric showers and u/floor leccy heating they are demanding alot more. Had a call out last winter where customers off supply, dno fuse on the pole had gone 60A on pole, 80A in dno head 80A switch fuse! They replaced it with 80.
 
Waw have you really installed another meter box next to dno box! If you have that is shocking imo. Put ur switch fuse in the dno box, if its on. The owners property its theirs not dno so you may add your sw fuse in there! Flobbogasted at that pic!!

Box on the right houses the gas meter you wally !
 
Just to stir the pot a little bit,

Why does the submain fuse need to discriminate with the service fuse?
Why shouldn't you have 2x 100A fuses in series?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
SWA, T&E or tails??
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
75

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Guest77,
Replies
75
Views
9,901

Advert