Evening all..

I am currently doing my first full rewire. The customer is having the wall knocked down with the meter/cutout and CU on it. the plan was to move the CU under the stairs and get DNO to move the supply to the same place. They have said they cannot move the cutout to where the CU will be. The approx length from cutout to CU will now be around 8m so I need to add a fused switch. My questions are about which type of cable to use:

1. I could use 2 core 25mm SWA (seperate 16mm earth) but I am unsure of how easy this is to bend through the route? It will be going straight up from the meter box and then 90degress into the house wall entering directly under the first floor floorboards. What is the best way to get it through the wall without putting too much strain on it (with regards bending angle)?

2. BS7671 states 25mm to be used, however I am fusing down to 80A, could I not use 16mm SWA as CCC is 87A?

3. Could I use tails as at no point will the tails be buried in the wall. They will be going directly under the floor boards from outside the house (suitable protected outside) and then down from the ceiling directly behind the new CU (there will be a cavity behind new CU as I will bring out from the wall). Do they need to be protected if they are not getting buried in the wall?

4. Which is easier to move around/use T&E (16mm or 25mm), SWA (16mm or 25mm) or tails?

5. Which is the best fused switch to use? KMF, wylex metal? Can I gland SWA into a KMF or does it need an adaptable box?

Cheers chaps:biggrin:
 
I wish I could find in BS7671 exactly where it states 25mm needs to be used?
I seem to remember that some DNOs would move a cut out a short distance if the consumer was disabled?
 
Last edited by a moderator:
I would preferably use 16mm 2 core SWA, fused down as you say. Never been keen on tails over such lengths running through a buildings fabric. You will be able to find out bending radii of the SWA online. The bigger casing on the Wylex switch fuses makes it a lot easier to terminate into. These ones: IMG_20150702_123302.jpg

Might be a bit of a swine to pull the SWA through though.
 
Evening all..

I am currently doing my first full rewire. The customer is having the wall knocked down with the meter/cutout and CU on it. the plan was to move the CU under the stairs and get DNO to move the supply to the same place. They have said they cannot move the cutout to where the CU will be. The approx length from cutout to CU will now be around 8m so I need to add a fused switch. My questions are about which type of cable to use:

1. I could use 2 core 25mm SWA (seperate 16mm earth) but I am unsure of how easy this is to bend through the route? It will be going straight up from the meter box and then 90degress into the house wall entering directly under the first floor floorboards. What is the best way to get it through the wall without putting too much strain on it (with regards bending angle)?
You would need to chase the brick out a bit to follow the bend then seal afterwards. Bending a cable that size isn't too much trouble with a couple of weetabix for brekky. I would be taking it down and under the ground floor as first choice though.

2. BS7671 states 25mm to be used does it ?, however I am fusing down to 80A, could I not use 16mm SWA as CCC is 87A? which table are you using for this data ?

3. Could I use tails as at no point will the tails be buried in the wall. They will be going directly under the floor boards from outside the house (suitable protected outside) and then down from the ceiling directly behind the new CU (there will be a cavity behind new CU as I will bring out from the wall). Do they need to be protected if they are not getting buried in the wall? Use SWA

4. Which is easier to move around/use T&E (16mm or 25mm), SWA (16mm or 25mm) or tails?

5. Which is the best fused switch to use? KMF, wylex metal? Can I gland SWA into a KMF or does it need an adaptable box? KMF will not accept a gland so you will need an extra box. Metal clad unit is less fiddly.

Cheers chaps:biggrin:

Remarks in red
 
I wish I could find in BS7671 exactly where it states 25mm needs to be used?
I seem to remember that some DNOs would move a cut out a short distance if the consumer was disabled?

ok, ok smarty pants! That OSG does have a lot to answer for!

To make bending the SWA easier, simply drill the hole through the wall on a angle.

Simple!! Cheers Dillb.
 
3- if at no point do the tails go buried in wall tails all the way! Still need a metal switch fuse being greater than 3M from meter! Is under stairs best design place for cu? What height will it be?
 
Personally I would rather move the board so it's closer to the cutout so that i didn't have to fuse it down, I would rather have the capacity in the supply should I want to add juicy appliances.
 
3- if at no point do the tails go buried in wall tails all the way! Still need a metal switch fuse being greater than 3M from meter! Is under stairs best design place for cu? What height will it be?
Have to agree. I'd never put a CU under the stairs. It's just isn't a good design.
 
Evening all..

I am currently doing my first full rewire. The customer is having the wall knocked down with the meter/cutout and CU on it. the plan was to move the CU under the stairs and get DNO to move the supply to the same place. They have said they cannot move the cutout to where the CU will be. The approx length from cutout to CU will now be around 8m so I need to add a fused switch. My questions are about which type of cable to use:

1. I could use 2 core 25mm SWA (seperate 16mm earth) but I am unsure of how easy this is to bend through the route? It will be going straight up from the meter box and then 90degress into the house wall entering directly under the first floor floorboards. What is the best way to get it through the wall without putting too much strain on it (with regards bending angle)?

2. BS7671 states 25mm to be used, however I am fusing down to 80A, could I not use 16mm SWA as CCC is 87A?

3. Could I use tails as at no point will the tails be buried in the wall. They will be going directly under the floor boards from outside the house (suitable protected outside) and then down from the ceiling directly behind the new CU (there will be a cavity behind new CU as I will bring out from the wall). Do they need to be protected if they are not getting buried in the wall?

4. Which is easier to move around/use T&E (16mm or 25mm), SWA (16mm or 25mm) or tails?

5. Which is the best fused switch to use? KMF, wylex metal? Can I gland SWA into a KMF or does it need an adaptable box?

Cheers chaps:biggrin:

HHD have the DNO explained why they won't move the supply? I've had similar things done. They normally take their cable back to the outside so the joint is 'accessible', joint a new section that is then long enough to reach the new point required. Recently had this done on a 3 phase supply into a house, the new run was about 5 meters.
 
Personally I would rather move the board so it's closer to the cutout so that i didn't have to fuse it down, I would rather have the capacity in the supply should I want to add juicy appliances.

Dont see how its relevant as op has stated db is gunna be 8M away so irrelevant! If you use a cable capable of taking the dno full service fuse isolate it at that rating
 
HHD have the DNO explained why they won't move the supply? I've had similar things done. They normally take their cable back to the outside so the joint is 'accessible', joint a new section that is then long enough to reach the new point required. Recently had this done on a 3 phase supply into a house, the new run was about 5 meters.

I dont think its set in stone that the supply will be moved to the outside, but I think its highly likely as that will be a much cheaper option for the customer. He may have to pay me more to extend the tails/SWA but I expect western power would have charged a great deal more than myself! The DNO options are to move it outside (outside wall is approx 30cm away from present supply) or to move it approx 6-7m (I think 8m was an exaggeration!) to the middle of the house.
 
Last edited:
With regards point 3, which is easier to manipulate.. SWA or tails? I'm assuming tails bend a little more than the equivalent sized SWA?
 

Reply to SWA, T&E or tails?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
397
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
676
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
727
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
547

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock