Excuse me? So your suggesting using dno full capacity in one post then slating use of it in another.? Why is it bad practice fusing your submain at same as dno cutout on a capable ccc cable,? Can u explain?


You never heard of discrimination?
 
You never heard of discrimination?

How would you go about achieving full discrimination between the DNO fuse and the one in the switch fuse then on a domestic setup such as the OP's? IMO it will be nigh on impossible.
 
Last edited by a moderator:
The total let through energy of the downstream fuse will have to be less than the pre-arcing energy of the upstream fuse to achieve full discrimination.
 
Last edited by a moderator:
Interesting discussion on discrimination, a question I've asked myself before, and received conflicting replies.

The meter box belongs to the owner of the property, but the DNO has certain requirements; BS 8567 (gas is BS 8499).

I asked my DNO (SSE) before on what they would expect to see in such a situation, as here. I asked DNO what would they say about extended tails, 'We would expect a switch fuse, as it is a submain'. Could I put equipment in said box, answer 'No not really, what are you thinking of? Switch fuse? 'Ahhh, okay'.

Considering size of fuse in switch fuse (i.e. DNO 100a, switch fuse 80a), I asked Elecsa tech support for advice;

'Without referring to the time current characteristics of each device for the exact information we believe that the fault protection characteristics of each device will be similar but not the same.

They do provide fault and overload protection for the whole installation. Therefore there will certainly some discrimination with overload protection.

The final decision regarding the discrimination of the two devices would be down to the designer of the installation'.
 
might be an idea to use a MCCB instead of a sw.fuse. cost permitting. this should ensure the MCCB tripping before the \DNO fuse. discuss?
 
might be an idea to use a MCCB instead of a sw.fuse. cost permitting. this should ensure the MCCB tripping before the \DNO fuse. discuss?

Mccb would clearly take out the supply before dno fuse. Domestically 80A is usially suffiecent but with some customers adding multiple electric showers and u/floor leccy heating they are demanding alot more. Had a call out last winter where customers off supply, dno fuse on the pole had gone 60A on pole, 80A in dno head 80A switch fuse! They replaced it with 80.
 
Just to stir the pot a little bit,

Why does the submain fuse need to discriminate with the service fuse?
Why shouldn't you have 2x 100A fuses in series?
 
But in the case of fault protection, could you be certain that an 80 would go before a 100, and in terms of supply, restricting owner to 80amps?
 
But in the case of fault protection, could you be certain that an 80 would go before a 100, and in terms of supply, restricting owner to 80amps?


Seriously?

come on now, how often have you seen over 80 amps being pulled on a supply for a long enough for it to blow the fuse under normal load conditions?
 
Seriously?

come on now, how often have you seen over 80 amps being pulled on a supply for a long enough for it to blow the fuse under normal load conditions?
As I said, posted the same question a while back, and this was one of the replies. I'm willing to be convinced either way.
 