Is it possible to put a 16mm swa on a 40a mcb protected by an rcd
If you look at the technical information from the MCB manufacturers website you should be able to obtain the maximum cable size that the device can accommodate, I think a typical 40A mcb will accept a 25mm cable but you need to check this. You will also need to check that the neutral and earth conductors can also safely be accommodated n their respective terminals. The issue normally with larger SWA cables is having sufficient space in the enclosure to gland and terminate the cable.
 
Cable calcs define your answer, is it 3m long or 300 hundred if you get my drift, your query is lacking context as to why you ask, if its simply terminal entry size then yes the mcb should accommodate a 16mm.
 
Or are you asking as it is SWA, and you may think a RCD is not required due to the SWA being earthed ?

It can be or certainly may be necessary/advisable depending on the connected load.
 
Its going to be feeding 2 ring circuits,2 lighting and 1 32a commando. The 2 ring circuits will never be running at the same time. The run will be about 11m and will be going on a 63a split rcd board.
 
It will just be rcd protected at the incoming point and then mcbs at the other end
Poor design. SWA doesn't need protection by a RCD, since there's very little likelihood of making contact with the live conductor, without shorting it to earth, in which case the OCD will take care of things.
Ideally this should be a fuse rather than a MCB, to provide discrimination between it and the MCBs or RCBOs at the load end.
 

Reply to Is it possible to put a 16mm swa on a 40a mcb protected by an rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
758
Replacing DB’s with all singing all dancing RCBO’s Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor...
Replies
11
Views
1K
The hottub is 8.1kw so will be 35A max output , I’m going to put it on 6mm 3core swa to an isolator then to the hottub. Would a 40a b type be...
Replies
5
Views
985
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
563
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
721

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock