The hottub is 8.1kw so will be 35A max output , I’m going to put it on 6mm 3core swa to an isolator then to the hottub. Would a 40a b type be sufficient for this ? Or would it be better to put it on a 40a c type mcb? Thanks
 
I’ve heard of some hot tubs having a spike when starting up and people thatve put them on a type c aswell as b just wanted to confirm what would be better
Does the manufacturer specify a particular protective device and will ADS be met with type c?

I'm asking questions as your profile indicates trainee status and OP provides insufficient information to provide an empirical answer.
 
While the 'hot' bit of a hot-tub load is resistive, there can be fairly beefy pumps for water jets and bubble jets, so I can understand there being a significant transient in load current if pumps are turned on while the heating element is running!
Edit: But as above, that doesn't mean bodging protection to avoid a problem!
 
Does the manufacturer specify a particular protective device and will ADS be met with type c?

I'm asking questions as your profile indicates trainee status and OP provides insufficient information to provide an empirical answer.
It is quite an old tub so doesn’t have the manufacturer instructions and cannot find out what it is, the only thing I could find on it is the max output that was 8.1ka
 

Reply to Hottub mcb selection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a small Consumer Unit fed from a 6 amp type B mcb to a 6 amp type B,it only feeds 1 light in a bin store . clearly we have no selectivity...
Replies
7
Views
587
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
547
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
414
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
631
Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock