Hello All...

My name's Wayne. I'm training to be an electrician and have loads of trivial questions that I hope you guys can help me out with.

Here goes with the first post:

Can someone explain in lovely simple language what is the difference between P.F.C. and P.S.C.C. and how do you calculate each one?

Thanks to all!!

Wayne :dizzy2:
 
Hello Can someone explain in lovely simple language what is the difference between P.F.C. and P.S.C.C. and how do you calculate each one?

Thanks to all!!

Wayne :dizzy2:

Hey PFC is perspective earth fault current which is the max current that can flow between live conductors to earth.

PSCC is perspective short circuit current which is the max current that can flow in a short between live conductors.

PEFC can be worked out roughly by dividing nominal voltage with Ze so

230Uo/0.35Ze = 460PFC

But it is not that accurate so is will need to be carrying out using a perspective fault current tester.

Good luck.
 
Thanks, Ducksy...short and sweet.

How accurate are the quoted figures for Ze? Is it best to measure by using instruments or believing the supplier? Thanks

Hey PFC is perspective earth fault current which is the max current that can flow between live conductors to earth.

PSCC is perspective short circuit current which is the max current that can flow in a short between live conductors.

PEFC can be worked out roughly by dividing nominal voltage with Ze so

230Uo/0.35Ze = 460PFC

But it is not that accurate so is will need to be carrying out using a perspective fault current tester.

Good luck.
 
How accurate are the quoted figures for Ze? Is it best to measure by using instruments or believing the supplier?

Well if you ask the DNO they will quote a tn-c-s as 0.35ohms and for tn-s its 0.8ohms..........in real life everyone uses a earth fault loop impedance tester to acquire Ze results.

wayne i would highly recommended a book called the electricians guide to the wiring regulations its got loads of information.
 
Thanks, Ducksy...Do you mean BS:7671?

Thanks again.

Wayne

Well if you ask the DNO they will quote a tn-c-s as 0.35ohms and for tn-s its 0.8ohms..........in real life everyone uses a earth fault loop impedance tester to acquire Ze results.

wayne i would highly recommended a book called the electricians guide to the wiring regulations its got loads of information.
 
Thanks, Ducksy...Do you mean BS:7671?

Thanks again.

Wayne
Ducksy means "The Electrician's Guide to the Building Regulations"
EGTBR 41Wdu0tAdUL._SL500_AA300_.jpgNote that the Building regulations have changed and Part P will change in April, however it still has a lot of useful and relevant information.
 
Last edited:
It's actually prospective (as in potential current under x fault) not "perceptive" (as in what you perceive depending on your position the fault current to be) Perspective of course differs depending on what side of the pond you stand so to speak, but in this circumstance, perspective is irrelevant, whereas the prospective or potential may change due to a number of variables.

And, hello, welcome to the forum chap
 

Reply to The lights are on!! in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
575
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
709
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
646
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
741

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock