Local caravan site, 16/2C swa out have 3 or 4 Electric points with 2 x 16amp sockets on one circuit protected by B63 MCB now, TNS system Main RCD 100/300 mA protecting MCBs, now I’m testing and getting Max Zs of 0.99 when permitted is 0.69 so pointlet de rating to 50 amp, I don’t like the idea of relying on just one RCD as we know there unreliable but we’re covered for 1667 ohms, now I’m doing an EICR there’s nothing wrong with it, i just want to know if you’d put Max Zs for RCD so 1667 or for the protective device.
Poor design my best bet is if they use a split gland plate or split the earthing from sub circuits I’d TNS the supply and TT the outgoing but I haven’t checked the rest of the panels but I guess they will be the same but some are only a year old.
Thanks
Poor design my best bet is if they use a split gland plate or split the earthing from sub circuits I’d TNS the supply and TT the outgoing but I haven’t checked the rest of the panels but I guess they will be the same but some are only a year old.