I have just looked in GN8 and it specifies that it is up to the designer to choose the value of current that is acceptable
0.5mA - perception threshold
10mA - let go threshold
30mA - <300ms muscle contraction, <5s breathing difficulty, revesible heart disruption, immobilization, but generally no organic damage.
The resistance of the human body approximating to 1kΩ gives resistance values of:
459kΩ for 0.5mA
22kΩ for 10mA
6.7kΩ for 30mA
since bonding faults could be reasonably long term in some cases I would tend to aim for 10mA as at least you can get away from the fault .
0.5mA - perception threshold
10mA - let go threshold
30mA - <300ms muscle contraction, <5s breathing difficulty, revesible heart disruption, immobilization, but generally no organic damage.
The resistance of the human body approximating to 1kΩ gives resistance values of:
459kΩ for 0.5mA
22kΩ for 10mA
6.7kΩ for 30mA
since bonding faults could be reasonably long term in some cases I would tend to aim for 10mA as at least you can get away from the fault .