Dear Colleagues, I have been discussing a situation with a young electrician I mentor. My electrical art is attached. Container A contains a Diesel generator whose output passes through a 300mA ELCB. Container B is a large refrigeration unit with integrated cooling machinery. The 5 cables between the containers are all the proper quality and toughness. It is a temporary arrangement while works are done on the onsite fridges/freezers. The containers are 2m apart and sitting on the same area of concrete though my drawing does not make that clear enough. Although I show the green bonding cable passing through the earth it does not - it is just the way I have drawn it.

The young electrician asked me if it was safe and compliant with whatever regulations apply to such an installation. I wondered what you thought and would say to him. I have already given my reply. Forgive me but I will not be saying anything further but will of course read what folk say.
 

Attachments

  • isocontainers.png
    isocontainers.png
    56.7 KB · Views: 75
Last edited:
I guess the obvious thing that is missing is a definite means of earthing, though it is almost a closed/isolated system as both containers are bonded together and it is not, I presume, offering power to any outside socket?

Cables between them would have to be armoured as no 30mA "additional protection" in case of damage, and indeed with the lack of definite earthing you could also argue ADS is missing from the design.

No doubt others will spot something I am missing, but not had my morning coffee yet!
 
  • Informative
Reactions: marconi
Actually there is a far bigger elephant in the room - the neutral is linked to earth at the load as well!

Not only breaking the RCD's operation but also forming a TN-C system against the regs (though with parallel paths far less risky then the copper-saving PEN conductor style).

See, never go looking for pachyderm before you have coffee!
 
  • Like
Reactions: marconi
Actually there is a far bigger elephant in the room - the neutral is linked to earth at the load as well!

Not only breaking the RCD's operation but also forming a TN-C system against the regs (though with parallel paths far less risky then the copper-saving PEN conductor style).

See, never go looking for pachyderm before you have coffee!
Thank you pc1966 - that is my drawing mistake. The N is not linked to the earth at the load in container B . See revised electrical art.
 

Attachments

  • corrected isocontainers.png
    corrected isocontainers.png
    56.1 KB · Views: 66
Last edited:
  • Like
Reactions: pc1966
I would treat it as a separate supply to the other containment & relevant Earthing systems to comply.
 
  • Like
Reactions: marconi

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

marconi

Mentor
Esteemed
Arms
Supporter
~
Joined
Location
London United Kingdom
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Two isocontainers sitting on the ground next to each
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
marconi,
Last reply from
cliffed,
Replies
4
Views
1,271

Advert