Do we all accept that an EICR is a report on the condition of an installation at the time of the Inspection and Testing?

Can anyone explain why either the water pipe or gas pipe would be used as an electrode, and then bonded?

Is 63Ohms a good or bad reading for an earth electrode?
Does it indicate any instability?

Finally, who believes that the outcome of the Further Investigation would lead to a code C1 or C2?

I see where you're going.

I would argue that the condition of an installation goes beyond just testing though. I could test something with a cracked case and hanging off the wall and still get a pass result. Who knows what state the electrode is in? If it's still even there and/or connected suitably.

And in any case, just because you're called out to issue an EICR doesn't mean that upon arrival you can't identify a problem worth addressing ahead of doing the EICR. It's not all about technically not doing anything wrong, it's about doing the right thing out of care for your customer too.

The outcome of further investigation would likely not result in C1 or 2. I fully expect that if the obstruction was removed the conductor would be revealed, connected soundly to a suitable electrode. But that's not the point. The point is that there is a chance it's not OK, and it's a chance the OP doesn't need to take.
 
It is the point though.
FI should be used for instances where it is suspected either a code C1 or C2 is present, but cannot be discovered for whatever reason.

This is copied from the notes on the 18th edition EICR model form:

“Where an observation requires further investigation (FI) because the inspection has revealed an apparent deficiency which could not, owing to the extent or limitations of the inspection, be fully identified and further investigation may reveal a code C1 or C2 item, this should be recorded within Section K, given the code FI and marked as unsatisfactory in Section E.”
 
It is the point though.
FI should be used for instances where it is suspected either a code C1 or C2 is present, but cannot be discovered for whatever reason.

This is copied from the notes on the 18th edition EICR model form:

“Where an observation requires further investigation (FI) because the inspection has revealed an apparent deficiency which could not, owing to the extent or limitations of the inspection, be fully identified and further investigation may reveal a code C1 or C2 item, this should be recorded within Section K, given the code FI and marked as unsatisfactory in Section E.”

Ok that's correct. I'm not saying there is cause to suspect a C1/C2. I am saying that if a critical part of the installation is inaccessible for visual inspection/maintenance, then that is a problem to fix ahead of testing.

The OP asked what code to use, and fair enough - there is no evidence to suspect it's unsafe. But there is also no evidence to conclusively prove it is safe. Safety would require both acceptable test results and also knowledge that what you're testing actually exists and exists in a state that can be expected to remain stable until the next test. So that for me is the first hurdle to jump: Fix the fact its inaccessible. In this case, a new rod.

I feel we're debating technicalities when we must all surely know that the connection in question shouldn't be hidden beneath a block of immovable concrete :D
 
Last edited:
If you don’t suspect a C1 or C2 code then you can’t possibly code something FI as by doing so you as the inspector suspect a potential danger is present but due to limitations you can’t see it.
If people give an FI for this then they must do when they can’t see a protective bonding conductor at the connected end of the gas or water but having confirmed the service has a low resistance to earth.
C3 for me
 
  • Agree
Reactions: 1 person
I know it's hindsight now, but you can always confirm bonding conductors with them disconnected using long lead test if unsure.

I think it just down to your judgement. As Ze is very acceptable, I would say either FI or LIM are perfectly reasonable.

Out of interest what sort of Zs's were you getting with bonds reconnected?
Zs's were around 8 ohms.
 
It is the point though.
FI should be used for instances where it is suspected either a code C1 or C2 is present, but cannot be discovered for whatever reason.
I’m amazed you’re saying this. It’s funny how IET wording can be interpreted. I fully understand the above point, but, stripping it back Further Investigation means exactly what it says on the tin to me, never mind what the ends of bells think who type all this carp up in an office stating it has to be used when a C1 or C2 is suspected.

Further Investigation means further investigation and this in my opinion warrants it. It’s not difficult to put a fresh accessible rod in and nor is it costly


“be fully identified and further investigation may reveal a code C1 or C2 item, this should be recorded within Section K, given the code FI and marked as unsatisfactory

I’ve taken a few lines out of the quote you have given from the book. That to me means FI and unsatisfactory IF the client is unwilling to add a fresh rod OR allow the actual further investigation which would lead to revealing the true identity, Condition and suitability of the Rod.

I stand by what I’ve always been taught and that is a Rod must be accessible for testing and maintenance.

I love debates like this, makes our trade interesting.
 
  • Agree
Reactions: telectrix
It is the point though.
FI should be used for instances where it is suspected either a code C1 or C2 is present, but cannot be discovered for whatever reason.
I’m amazed you’re saying this. It’s funny how IET wording can be interpreted. I fully understand the above point, but, stripping it back Further Investigation means exactly what it says on the tin to me, never mind what the ends of bells think who type all this carp up in an office stating it has to be used when a C1 or C2 is suspected.

Further Investigation means further investigation and this in my opinion warrants it. It’s not difficult to put a fresh accessible rod in and nor is it costly


“be fully identified and further investigation may reveal a code C1 or C2 item, this should be recorded within Section K, given the code FI and marked as unsatisfactory

I’ve taken a few lines out of the quote you have given from the book. That to me means FI and unsatisfactory IF the client is unwilling to add a fresh rod OR allow the actual further investigation which would lead to revealing the true identity, Condition and suitability of the Rod.

I stand by what I’ve always been taught and that is a Rod must be accessible for testing and maintenance.

I love debates like this, makes our trade interesting.
 
I’ve taken a few lines out of the quote you have given from the book. That to me means FI and unsatisfactory IF the client is unwilling to add a fresh rod OR allow the actual further investigation which would lead to revealing the true identity, Condition and suitability of the Rod.

I stand by what I’ve always been taught and that is a Rod must be accessible for testing and maintenance.

I love debates like this, makes our trade interesting.
i agreed with the previous post, but sod it. not bothering with the duplicate. too much effort. :p:p:p:p:p:p.
 
  • Funny
Reactions: markc123
Because for reasons laid out it could be testing fine today, and under different circumstances it would fail.

No one knows what it's connected too nor the condition of it. Just because it's technically passed doesn't mean it's common sense to make assumptions about it's actual suitability or safety. That's over reliance on testing imo.

Perhaps a better approach: If you don't know what you're testing, solve that problem first. Then test.

You cannot see the cables in the wall but we do not assume thay are wrong unless proved by testing.

No different here.
 
  • Like
Reactions: Rpa07
You cannot see the cables in the wall but we do not assume thay are wrong unless proved by testing.

No different here.

It's totally different. You know it's a cable, you can easily access at least one end of it. You can identify the cable type and check it's suitable. Even if technically a length of cable is hidden between two concealed boxes on a circuit, you can still check that it exists by testing what you can access.

It is however possible the electrode does not exist, or is not connected. That cannot be confidently revealed by testing alone.
 
You cannot see the cables in the wall but we do not assume thay are wrong unless proved by testing.

No different here.

It absolutley is different.

Fault on circuits - breakers trip.

Main earth not stable - zs’s not stable - potentially for MCBS not to trip under fault conditions.

Can’t compare the main earth to circuits IMO. The problem with the main earth is that once it’s failed it could be too late and there isn’t any warning.

The main earth needs to be accessible for maintenance and testing. Period.
 
  • Agree
Reactions: Deuce
It absolutley is different.

Fault on circuits - breakers trip.

Main earth not stable - zs’s not stable - potentially for MCBS not to trip under fault conditions.

Can’t compare the main earth to circuits IMO. The problem with the main earth is that once it’s failed it could be too late and there isn’t any warning.

The main earth needs to be accessible for maintenance and testing. Period.

That's another angle that keeps being skipped as people try to compare this to other situations.

This isn't a protected component... it IS the protection. We can all appreciate that houses get pulled around and often access to certain parts of the electrical installation are a nightmare, sometimes it's simply more practical to go on the weight of evidence, testing, and in the end to assume something is fine and there is no need for further investigation. But if you get ONE thing right, absolutely beyond a shadow of a doubt. Get the earthing of the entire house right.

Question I suppose... Would you bet your life the electrode is present, correct and suitably attached? I wouldn't so I certainly wouldn't bet the life of my customer. I would bet £1000 it's all there, maybe more - I would almost certainly make a tidy return on that bet :)

But not a life. That's my stance.
 
Last edited:
  • Agree
Reactions: markc123
Helluva speech deuce, I reckon that sums up the answer to this thread!

Thanks :D

To be fair, I think a lot of folk want to argue specific technical points on these forums - which is fine, I do it too.

But on this occasion I can't accept there is any correct resolution other than starting by sinking a new rod. Any other debate about how to correctly evaluate the current situation is secondary to me. And I'm wondering why the OP hasn't come back yet to say they have had that conversation with the customer.
 
So if there’s a 10mm connected in the dB say for the protective bonding conductor to the gas but you can’t confirm the connection at the gas end where it’s connected (built in to the fabric of the building), you do a R2 test on the pipework with all parallel paths disconnected as far as reasonably practicable, you get a reading of say 0.03 ohms, do you FI the fact you can’t see the connection for inspection and testing purposes?
Bare in mind that all though it’s not the principle form of earthing to the installation it’s importance that the bonding is present and connected is paramount for ADS.
 
  • Like
Reactions: Nigel
Personally I would FI any bonding incoming gas/water pipes if connection not visible/accessible to be able to remove and get an R2 to confirm. Otherwise what's to say the 10mm from board is connected to the pipe at all? and that your reading on the pipe isn't just a parallel path that hasn't been found/disconnected?
Normally on a EICR form there is simply a pass or fail tick box for condition/accessibility to bonding connections so if I can't see it.....its a fail. Simple!
 
  • Disagree
Reactions: 1 person
There is no pass or fail box, it’s a tick for confirmation of an acceptable test of continuity.
In the schedules of inspections there’s a box for the condition and accessibility of the bonding conductors and it’s outcome.
A tick or a suitable code if applicable
So for an FI code you think that there’s potential or immediate danger.
Even tho a continuity test has confirmed a low resistance to earth.
Depending on the reading say 0.03 ohms you could even calculate if it’s a realistic value depending on the estimated cable run from the dB to the gas service.
A reading so low is unlikely to be from another circuits cpc in my opinion.
Just my take on it
 
Last edited by a moderator:
  • Agree
Reactions: Rpa07
Fair enough a tick box for confirmation of continuity. But can you confirm continuity without disconnecting and doing an R2 to prove its not broken?
If I can't see it to remove it, then I can't confirm, therefore I give it a code FI. Or am I being too harsh?
 
Fair enough a tick box for confirmation of continuity. But can you confirm continuity without disconnecting and doing an R2 to prove its not broken?
If I can't see it to remove it, then I can't confirm, therefore I give it a code FI. Or am I being too harsh?
It’s one of them isn’t it?
It’s down to the inspector at the end of the day and it’s clear we all have different opinions so maybe there’s no right or wrong answer and you have to justify your actions with yourself.
It’s usually the kitchen fitters fault for boxing over the pipework so let’s blame him
 
  • Funny
Reactions: markc123
Fair enough a tick box for confirmation of continuity. But can you confirm continuity without disconnecting and doing an R2 to prove its not broken?
If I can't see it to remove it, then I can't confirm, therefore I give it a code FI. Or am I being too harsh?
Well, if you believe there is no earthing (which would warrant a code C2), then your FI would be fair.
 
It's totally different. You know it's a cable, you can easily access at least one end of it. You can identify the cable type and check it's suitable. Even if technically a length of cable is hidden between two concealed boxes on a circuit, you can still check that it exists by testing what you can access.

It is however possible the electrode does not exist, or is not connected. That cannot be confidently revealed by testing alone.

Is there a specified type of electrode that can only be used?
 
It absolutley is different.

Fault on circuits - breakers trip.

Main earth not stable - zs’s not stable - potentially for MCBS not to trip under fault conditions.

Can’t compare the main earth to circuits IMO. The problem with the main earth is that once it’s failed it could be too late and there isn’t any warning.

The main earth needs to be accessible for maintenance and testing. Period.

A TT would not be relying on MCBs for fault protection due to the unreliable earth.
 
Personally I would FI any bonding incoming gas/water pipes if connection not visible/accessible to be able to remove and get an R2 to confirm. Otherwise what's to say the 10mm from board is connected to the pipe at all? and that your reading on the pipe isn't just a parallel path that hasn't been found/disconnected?
Normally on a EICR form there is simply a pass or fail tick box for condition/accessibility to bonding connections so if I can't see it.....its a fail. Simple!

Mental.
 
Is there a specified type of electrode that can only be used?

I don't know why you would need to ask that question..? You have argued a somewhat minority view on this thread, and resorted to ever more peripheral technicalities to make your point. And now you ask me a rather basic question about the selection of electrode?

Anyway, any type is fine so long as it's installed as per regulation. But in some places, certain materials could prove a very poor choice long term. That's a great reason to leave them accessible, for visual inspection. Corrosion tends to occur top down initially as this is where the material has most access to air, the lower part being effectively in an anaerobic enclosure. Although in the end the corrosion will spread uniformly. This means there is a good opportunity to get an early warning if the material selected is corroding much faster than would be expected.

As corrosion will start top down, it's also useful to be able to see the clamp to check for corrosion around it's contact area with the electrode.

And once again, in this case - it would also be useful to know it actually exists and is still connected.
 
  • Like
Reactions: KevinH
I don't know why you would need to ask that question..? You have argued a somewhat minority view on this thread, and resorted to ever more peripheral technicalities to make your point. And now you ask me a rather basic question about the selection of electrode?

Anyway, any type is fine so long as it's installed as per regulation. But in some places, certain materials could prove a very poor choice long term. That's a great reason to leave them accessible, for visual inspection. Corrosion tends to occur top down initially as this is where the material has most access to air, the lower part being effectively in an anaerobic enclosure. Although in the end the corrosion will spread uniformly. This means there is a good opportunity to get an early warning if the material selected is corroding much faster than would be expected.

As corrosion will start top down, it's also useful to be able to see the clamp to check for corrosion around it's contact area with the electrode.

And once again, in this case - it would also be useful to know it actually exists and is still connected.

I am sorry mate but you are talking absolute tosh. You have presented zero evidence to back up your stance other than that you want to see it.

I agree a C3 but would you dig up the complete rod to inspect it on every EICR? I mean who knows what the state could be under ground. Surely you would want to check the whole rod?

Also you would want to inspect fully every cpc throughout the installation. I mean it could go to anywhere once in the wall couldn’t it?
 
I am sorry mate but you are talking absolute tosh. You have presented zero evidence to back up your stance other than that you want to see it.

I agree a C3 but would you dig up the complete rod to inspect it on every EICR? I mean who knows what the state could be under ground. Surely you would want to check the whole rod?

Also you would want to inspect fully every cpc throughout the installation. I mean it could go to anywhere once in the wall couldn’t it?

You asked a question, I answered.

I never suggested anything about digging up the rod to inspect it. You're reacting very quickly to what you think I'm saying, please read more thoroughly.

I also never gave any opinion on the c3. At any point.

All I have stated is my opinion that as the rod is now totally inaccessible it should just be a new rod. It's ok if you disagree but at least remain polite. Especially when I was only answering a question you asked to the best of my knowledge.
 
  • Like
Reactions: Ricky103

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Unable to find earth rod when doing EICR
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
68

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Deuce,
Replies
68
Views
17,067

Advert