Sample Questions C&G 2392-10 Certificate in Fundamental Inspection & Testing - paper 2

( 1 ) The person who tests and signs the Electrical Installation Certificate for an Electrical Installation should be ?
A – The owner of the Installation ,
B – The Electrical Contractor who carried out the work ,
C – A representative of the Owner of the premises ,
D – A Competent person from an inspection and test company ,

( 2 ) Before commencing an initial inspection and test , the inspector should have a copy of the ?
A – Heath and Safety at Work Act ,
B – Electricity at Work regulations 1989 ,
C – Guidance Note 1 – Selection and Erection ,
D – Installation Specification ,

( 3 ) Which of the following information is “ Not “ required by the person carrying out the inspection and test ?
A – The prospective fault current at the origin of the installation ,
B – The external loop impedance ( Ze ) ,
C – information on the manufacturer of the electrical equipment used in the ,
D – the method used for fault protection ,

( 4 ) Which of the following should accompany the inspection and test ?
A – two copies of test results ,
B – copies of the inspection and test schedules ,
C – copies of minor works certificates ,
D – invoices for any remedial work carried out ,

( 5 ) Which of the following statement is false ?
A – Inspection & Testing may be done in an order decided by the test engineer ,
B – Installations must be inspected and tested on completion and also during erection ,
C – The purpose of the inspected is to verify equipment is correctly selected and erected in accordance with BS7671 ,
D – Precautions shall be taken to avoid damage to property during Inspection & Testing ,

( 6 ) Which one of the following does not need to be checked for compliance during the visual Inspection of an installation , ?
A – Presence of fire barriers ,
B – Correct connection of the supply authority’s fuse ,
C – Routing of cables in safe zone ,
D – Connection of single pole device in phase conductors’ only ,

( 7 ) A visual Inspection is necessary before testing to check whether ?
A – There is adequate access to switchgear ,
B – The Zs is within the maximum allowed ,
C – The polarity of switches’ and fuses are correct ,
D – The insulation resistance is acceptable ,

( 8 ) The top surface of a consumer unit should be protected from ingress of dust to a standard of ?
A – IP2X B – IP4X C – IP5X D – IP6X

( 9 ) During Inspection of a distribution board containing exposed conductive parts it should be verified that ?
A – The board is situated at least 2 meters above ground level ,
B – The board has a handle and the door is shut ,
C – The door can only be opened with a key or tool ,
D – The board has at least ingress protection to IP2X ,

( 10 ) When inspecting a conductor used for circuit protection it must be verified that the conductor is ,
A – Green or green and yellow throughout its length ,
B – green and yellow for at least 100mm at both ends ,
C – Marked with numerals at both ends ,
D – Green and yellow throughout its length ,

( 11 ) Which one of the following tests can only be carried out after supply is connected ,
A – Earth fault loop impedance ,
B – Insulation resistance ,
C – Polarity , D – Continuity of the protective conductors’ ,

Sample Questions C&G 2392-10 Certificate in Fundamental Inspection & Testing - paper 2

( 12 ) The minimum test voltage that should be applied when testing the insulation resistance of a SELV circuit is , ?
A – 500v - dc B – 500v - ac C – 250v - dc D –250v - ac

( 13 ) Given the following numbered tests, select the sequence in which these tests should be conducted for a new installation : ?
1 , functional , 2 , insulation resistance , 3 , polarity , 4 , continuity of final ring conductors’ , 5 , continuity of protective conductors’
A – 1,3,4,5,2, B – 4,5,3,2,1, C – 5,4,2,3,1, D – 2,3,4,5,1,

( 14 ) Insulation resistance testers are designed to measure ?
A – High resistance using an ac voltage ,
B – Low resistance using an ac voltage ,
C – Low resistance using an dc voltage ,
D – High resistance using an dc voltage ,

( 15 ) An approved voltage tester can be used to ?
A – Establish whether a circuit conductor is live or not ,
B – Determine the effectiveness of a disconnection device ,
C – Measure the resistance of an earth continuity conductor ,
D – Carry out continuity tests ,

( 16 ) The purpose of the test button of residual current device is to check the ?
A – Earth fault loop impedance ,
B – Continuity of the earthing conductor ,
C – Earth electrode resistance ,
D – Mechanical operation of the rcd ,

( 17 ) Statement 1, – A polarity test is carried out with a loop tester , Statement 2 , A polarity test can confirm correct connection of conductors within an Edison screw lamp
A – Statement 1 is true , Statement 2 is false ,
B – Both Statement are true ,
C – Statement 1, is false , Statement 2 is true ,
D – Both Statement are false ,

( 18 ) Which one of the following tests should be conducted to verify protection by electrical separation of ELV and LV circuits ?
A – Verification of protection by barriers or enclosures to minimum of IP5X
B – An insulation resistance test at 500v dc , between ELV and LV circuits ,
C – testing between conductors’ of each ELV circuit at 250v dc ,
D – An insulation resistance test between ELV and LV circuits at 250v dc

( 19 ) The schedule for an electrical installation should include the following ?
A – Date of completion
B – Recommended dates for future periodic testing ,
C – BS numbers of all equipment within the installation ,
D – The rating and type of protective devices ,

( 20 ) For circuits having a nominal voltage of 230v , the minimum insulation resistance required is ?
A – 5.0 MΩ B – 1.0MΩ C – 0.5MΩ D – 0.25MΩ

( 21 ) When an Electrical Installation Certificate is issued , any defects or Omissions must be ?
A – Made good
B – Identified
C – Noted on the certificate
D – Notified to the client

( 22 ) The maximum earth loop impedance to BS 7671 : 2008 for a circuit protected by a 20A BS-88 ( gG )
Fuse given a 5 second disconnection time is ?
A – 7.42 Ω B – 2.91 Ω C – 1.84 Ω D – 1.35 Ω

( 23 ) The maximum disconnection time allowed for a TN systems with a nominal voltage of 250v ac , to earth is ?
A – 0.2 seconds B – 0.4 seconds C – 1 seconds D – 5 seconds

( 24 ) What is the maximum earth fault loop impedance allowed when using a 32A Type C circuit breaker
Giving a disconnection time of 5seconds , the nominal voltage to earth ( Uo ) is 55V ,
A – 0.34 Ω B – 0.40 Ω C – 0.17 Ω D – 0.09 Ω

Sample Questions C&G 2392-10 Certificate in Fundamental Inspection & Testing - paper 2

( 25 ) A insulation resistance test is carried out on a single-phase 230v circuit, the minimum acceptable reading and correct test voltage to BS 7671 : 2008 should be ?
A – 0.5 MΩ and 250v dc , B – 1.0 MΩ and 500v dc , C – 0.5 MΩ and 500v dc , D – 2.0 MΩ and 500v dc ,

( 26 ) A circuit has an external earth loop impedance Ze of 0.6 Ω , the maximum value of ( R1 + R2 ) to BS 7671 : 2008 , on a circuit protected by a Type B 32A circuit breaker giving a 0.4 seconds disconnection time will be ?
A – 1.44 Ω B – 2.04 Ω C – 0.84 Ω D – 0.24 Ω

( 27 ) Any faults or defects identified an initial verification should be ?
A – Made good immediately ,
B – Noted on the certificate before issuing it to the client ,
C – Noted on the certificate and arrange to complete repairs ,
D – Made good before issuing the certificate ,

( 28 ) The type of certificate is issued after installing an additional socket outlet within an existing installation would be a ?
A – Minor Certificate ,
B – Verification and Test Certificate ,
C – Installation Certificate ,
D – Periodic Test Certificate ,

( 29 ) Which of the following tests is carried out on a “ live “ circuits ,
A – Insulation resistance ,
B – Earth fault loop impedance ,
C – Continuity of final ring circuit conductors ,
D – Polarity by Continuity methods ,

( 30 ) End-to-end resistance checks would be carried out on a ,
A – Radial circuit ,
B – Lighting circuit ,
C – Ring final circuit ,
D – Fused connection unit ,


( 1 )- B ( 2 )- D ( 3 )- C ( 4 )- B ( 5 )- A ( 6 )- B ( 7 )- A ( 8 )- B ( 9 )- C ( 10 )- D ( 11)- A ( 11) - A ( 12 )- C ( 13 )- C
( 14 )- D ( 15 )- A ( 16 )- D ( 17 )- C ( 18 )- B ( 19 )- D ( 20 )- B ( 21 )- A ( 22 )- B ( 23 )- A ( 24 )- C ( 25 )- B ( 26 )- C ( 27 )- D ( 28 )- A ( 29 )- B ( 30 )- C

( 24 ) What is the maximum earth fault loop impedance allowed when using a 32A Type C circuit breaker
Giving a disconnection time of 5seconds , the nominal voltage to earth ( Uo ) is 55V ,
A – 0.34 Ω B – 0.40 Ω C – 0.17Ω ↔ ( regs : 41.6 ) ۝ D – 0.09 Ω

Ps , they is a very very small little red heron in here guess which one , the clock is ticking ? :)
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Useful information
Prefix
N/A
Forum
Electrician Courses : Electrical Quals
Start date
Last reply date
Replies
20
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
amberleaf,
Last reply from
Deleted member 26818,
Replies
20
Views
27,854

Advert

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.