Hi

Is there any advantage to using SWA cable for a distribution circuit to a DB, instead of eg. using singles in trunking? Let's say the sub board is in the same building as the main board.

It's just whenever I see descriptions of distribution circuits, they seem always to be in SWA (even if not buried underground) and I'm not sure why.

Not a real world problem, I'd like to know for an assignment.

Thanks
 
In an industrial situation, using steel conduit or trunking is exactly the same as swa, in practical terms though most will carry swa in stock, whilst not the larger cable sizes in singles which are likely to be larger cross section than xlpe swa.

In a residential situation however, in practice the cables would require rcd protection unless run in steel conduit or via swa.
 
By running a seperate cable you can reduce (or even avoid) the need for grouping factors to be applied to both the distribution circuit and the final circuits.

Distribution circuits can be run in singles, and indeed they sometimes are, especially if it is a shortish distance.

Running large circuits in trunking can also dramatically increase the required size of trunking plus it can be a pig to get the cables round bends!
 
Unless you have trunking in for other reasons, it is far cheaper/faster/easier to run a length of SWA in.

If you do find yourself running large singles in trunking then using flexible tri-rated will make your pain less, subject to proper use of ferrules and crimp lugs to match!
 
By running a seperate cable you can reduce (or even avoid) the need for grouping factors to be applied to both the distribution circuit and the final circuits.

Distribution circuits can be run in singles, and indeed they sometimes are, especially if it is a shortish distance.

Running large circuits in trunking can also dramatically increase the required size of trunking plus it can be a pig to get the cables round bends!
Thank you Davesparks, I hadn't even thought about grouping. Very useful post, thanks.
[automerge]1595443421[/automerge]
Unless you have trunking in for other reasons, it is far cheaper/faster/easier to run a length of SWA in.

If you do find yourself running large singles in trunking then using flexible tri-rated will make your pain less, subject to proper use of ferrules and crimp lugs to match!
Thank you pc1966 for the info. I'm pretty sure I will go with swa. Am now going to look up flexible tri-rated though. It could be the one I want for some of the other circuits! I wonder if it comes under the classification of 'flexible cable' rather than 'unsheathed' (for those tables)...thanks again, suki
 
I wonder if it comes under the classification of 'flexible cable' rather than 'unsheathed'
Normally I would consider them as for singles.

Often tri-rated is OK to 105C (UL rating) or 90C (BS 6231 rating) but most accessories are not, so you might be safest to use tables for 70C singles if that is what the end points are safe to.
 
Distribution circuits often travel a significant distance through a building, further than a typical final circuit. Once each circuit leaves the area of the main DB, it is likely to be the only cable following that route. Therefore, a sheathed cable that requires no time-consuming or costly containment to protect it is likely to be the most practical and economic option.

Singles in trunking come into their own when many circuits are to be run along the approximately the same route. The time and cost of erecting the trunking is then justified by avoiding the need to make off each SWA, and of course much neater. Compartment trunking can serve other types of cabling too e.g. data and alarm, further justifying its cost.
 
Distribution circuits often travel a significant distance through a building, further than a typical final circuit. Once each circuit leaves the area of the main DB, it is likely to be the only cable following that route. Therefore, a sheathed cable that requires no time-consuming or costly containment to protect it is likely to be the most practical and economic option.

Singles in trunking come into their own when many circuits are to be run along the approximately the same route. The time and cost of erecting the trunking is then justified by avoiding the need to make off each SWA, and of course much neater. Compartment trunking can serve other types of cabling too e.g. data and alarm, further justifying its cost.
Thank you for this interesting post, Lucien Nunes. The way you've articulated this has improved my grasp of how this works. Thanks!
 

Reply to Why use SWA to feed DBs? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
703
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
629
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...
Replies
26
Views
3K
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock