I've just re-read this thread, and it seems that the distance to the distribution TX is some 250 metres. We don't know the size of the TX though!! I would have to say that the supply cables would have to be sizable to allow a Ze of 0.01 ohm and a PFC of 19+KA. I would suggest that measurements taken have a largish error factor within them... You would only expect to see around 16KA in central London's DNO extensive networks.

250 metres is a fair distance, and when taking into account all the resistances/impedances of connections, switch gear, and cables etc, it's going to be highly unlikely that the given figures are anywhere near correct. Going by those figures the TX would have to be 1000 KVA, which would normally be capable of providing around 20KA into a fault at it's LV terminals, but very doubtful 250 metres distant, passing through all those said impedances...

To be totally honest, you would only find those figures within the actual sub-station itself or very, very close to it.
 
Took a while to get an answer to my original question, so thank you E54 for your last post! I was hoping someone was going to say that.

I hope to get the opportunity to take my own measurements sometime soon - I hate it when I suspect something is wrong, and cannot rest until i get to the bottom of it. My previous musings about SSC and HRC carriers were me trying to establish a plan B, just in case. Hopefully it won't come to that.
 

Reply to Ze and distance from substation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Over the last few days, I have stumbled across a number of threads that seem to point to a prevalent misunderstanding. Either that, or I have been...
Replies
6
Views
2K
Another long one from me ... I hope that it covers all the bases and is a more thorough approach to the subject. It is my first design work so...
Replies
44
Views
6K
G
Hi So today i tested at the orgin of the installation and on my MFT 1552 Megger, i got a reading of <0.01 for Ze and >19.9 KA for PFC, it's a...
Replies
6
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock