C

crow11

fitted a new c/u and put a new ring main in kitchen last week ready for my assessment in the morning, everything tested ok and zs tested ok then, sent meter in for calibration check last thursday and picked it up today (megger 1552) certificate says everything passed no adjustment needed, so i thought i would go back to the job and just redo some basic testing and now for some reason it won't let me do a zs test just keeps tripping the 63A rcd, r1 + r2 + rn and R1+R2 are all the same as when i tested last week as is ir and continuity, nothing as changed at the job at all, iv'e switched every other circuit of and unplugged everything and just left the new ring main switched on with everything unplugged and still trips the rcd, tried it on the other side and it trips that rcd as well, it will let me do a no trip 3 lead zs but just totally baffled as to why it now trips it out on the normal zs test
 
Sounds like its working fine, my tester always trips RCDs unless I use the no trip function.
 
  • Like
Reactions: 3 people
fitted a new c/u and put a new ring main in kitchen last week ready for my assessment in the morning, everything tested ok and zs tested ok then, sent meter in for calibration check last thursday and picked it up today (megger 1552) certificate says everything passed no adjustment needed, so i thought i would go back to the job and just redo some basic testing and now for some reason it won't let me do a zs test just keeps tripping the 63A rcd, r1 + r2 + rn and R1+R2 are all the same as when i tested last week as is ir and continuity, nothing as changed at the job at all, iv'e switched every other circuit of and unplugged everything and just left the new ring main switched on with everything unplugged and still trips the rcd, tried it on the other side and it trips that rcd as well, it will let me do a no trip 3 lead zs but just totally baffled as to why it now trips it out on the normal zs test

Hi Crow..

Think I must be getting this a bit wrong as a bit confused! Are you saying that you get a Zs reading when you test on the 'No trip' function? If you are then just use that result. Its always going to trip the RCD if you dont use the 'no trip' function. The 'normal' Zs function on the MFT is for circuits that are not on an RCD.
 
on RCD circuits you must use 3 lead no trip setting with a 1552. or the RCD will trip
 
you have to use no trip when rcd involved
 
on RCD circuits you must use 3 lead no trip setting with a 1552. or the RCD will trip

I have NEVER managed to reply to a thread before you Tel. I am in shock! :dizzy2:
 
It's sad star if affairs when you can't grasp it, just push the button write then number down doesn't work for me nursey:)))
 
  • Like
Reactions: 1 person
Sounds like his MFT was possibly faulty pre-cal and they've tweaked it without telling him.
 
I have NEVER managed to reply to a thread before you Tel. I am in shock! :dizzy2:



first for everything, mate. and if you are in shock, you've fitted the RCD the wrong way round. :lipsrsealed2:
 
  • Like
Reactions: 1 person
Do you get what I'm saying vw camper man
 
P=IU, I think he's looking a bit more deeply, i.e. why has it changed, if it's OK now then perhaps it was giving wrong results before.

So I think the specific question would be 'Why did my MFT not trip the RCD when I was doing high current Zs tests, until its recent calibration, despite the fact they claim not to have done anything to it.' That is a good question but you don't know for certain whether the MFT or the RCD behaviour is changed. You might be onto a loser trying to explain it, although if it were me I'd try to get access to another RCD that I had done a test on in the recent past, and verify the accuracy of the results with the tester as it is now. Just in case it was not operating correctly. Did any of the results look odd, before the calibration?
 
  • Like
Reactions: 1 person
it's quite possible that the OP has slipped up. may have been doing readings using the plug in lead, not realising that it was a 3 lead test and now , post calibration has been using the probes. does that make sense?
 
think archy might be right in his theory, before calibration test it would do a zs test on a rcd circuit, so can only think something as been adjusted on calibration test, cause since i got it back it won't, i had a calibration check at the same place last year and it still did zs ok then on rcd circuits, i must of had a special megger lol cause the reading for the zs where what you would expect them to be so it wasn't like it was giving me false readings
 
i know what you mean tel, but no still doing it the same way as before, kewtech plug in adapter using 2 leads, just one of those mysteries i suppose
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
zs test keeps tripping rcd
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
crow11,
Last reply from
Deleted member 72666,
Replies
16
Views
7,747

Advert